If you can maintain 22" deflector then it doesn't matter if what type of
obstructed construction you have as long as they are within 1 to 6
inches of the bottom. It's not a specific application until you exceed
the 22 inch deflector in concrete tees.

Split this hair. Special application #2 mentions a "horizontal plane 1
inch beneath the bottom of the tees". The EC criteria #2 for obstructed
says "with a deflector location below structural members and a maximum
of 22 inches". Since it doesn't mention horizontal plane does it mean
that the head has be located directly under, not in between a structural
members?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Geoff
Dyce
Sent: Tuesday, October 27, 2009 6:50 AM
To: [email protected]
Subject: RE: Tyco EC 14 & Double Tee's

Hey Chris.  Not a problem I guess when it comes from the company.  I
just
completed a job almost identical to this string.  My tees were only 22"
deep
but were 60-0 in lgth.  I went to Tyco literature and it pretty much
disagrees with what they told you on the phone.  I followed their
submittal
data.......TYCO-Tech Data-Extended Coverage-TFP220 (EC14's)-pg
4-Concrete
tees item #1.
Tell me I'm wrong because I would love to use EC hds but I interpret
this
spec for what it says.  Thanks
Geoff

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Tuesday, October 27, 2009 9:40 AM
To: [email protected]
Subject: RE: Tyco EC 14 & Double Tee's

Well all I relayed is what Tyco told me < 2 hours ago.  A 58' long tee's
in
my case with only a 22" stem would not require baffles with the use of
EC14's.  Ken was quick and certain like he fielded this question before.


Chris 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Geoff
Dyce
Sent: Tuesday, October 27, 2009 8:33 AM
To: [email protected]
Subject: RE: Tyco EC 14 & Double Tee's

Chris.  Over 32 ft in lgth, with EC heads, you will need baffles.  Says
so
in the specs!  It does not say this for 5.6 or 8.0 std or QR sprks.  I
believe the 32-0 lgth is the deciding factor for EC heads.
G

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Tuesday, October 27, 2009 8:51 AM
To: [email protected]
Subject: RE: Tyco EC 14 & Double Tee's

Just got off the phone with Tyco.  FYI if you can keep a 22" deflector
you
do not need to look at the special application stuff.  So depending on
stem
oc dimensions you might get to 22-24" deep before you have to go with
baffles.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Geoff
Dyce
Sent: Tuesday, October 27, 2009 7:37 AM
To: [email protected]
Subject: RE: Tyco EC 14 & Double Tee's

Just an opinion but EC hds. require the baffles as noted for, I believe,
all
mfgrs. EC heads in concrete tee construction.  If you look at regular QR
sprks and not EC, it does not appear that you need baffles.
G
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Monday, October 26, 2009 5:05 PM
To: [email protected]
Subject: Tyco EC 14 & Double Tee's

In the Design Criteria these heads are listed for the generic obstructed
construction.  Great, 1-6" down 22" max etc.  But then there is a
special
application for concrete tee's that gives you up to 31" down if you meet
all
the other criteria.  Think baffles 32' o.c. 

 

So the question is if I can hold the 22"  and meet the normal
obstruction
rules can I use these under tee's like normal obstructed construction or
do
I still have to use the special application requirements?  (Tyco is
closed
for the day)

 

I think the answer is yes.  I think the special application is only for
an
exception to the "exception" that allows 22" down compared to the normal
1-12".  But I can read it either way.  In this case I'd like to stick
with
22" because I can with the particulars on the job.  So I have a biased
opinion. 

 

And I'm only bidding so not in a pinch (yet).        

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to