Well all I relayed is what Tyco told me < 2 hours ago. A 58' long tee's in my case with only a 22" stem would not require baffles with the use of EC14's. Ken was quick and certain like he fielded this question before.
Chris -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Geoff Dyce Sent: Tuesday, October 27, 2009 8:33 AM To: [email protected] Subject: RE: Tyco EC 14 & Double Tee's Chris. Over 32 ft in lgth, with EC heads, you will need baffles. Says so in the specs! It does not say this for 5.6 or 8.0 std or QR sprks. I believe the 32-0 lgth is the deciding factor for EC heads. G -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Tuesday, October 27, 2009 8:51 AM To: [email protected] Subject: RE: Tyco EC 14 & Double Tee's Just got off the phone with Tyco. FYI if you can keep a 22" deflector you do not need to look at the special application stuff. So depending on stem oc dimensions you might get to 22-24" deep before you have to go with baffles. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Geoff Dyce Sent: Tuesday, October 27, 2009 7:37 AM To: [email protected] Subject: RE: Tyco EC 14 & Double Tee's Just an opinion but EC hds. require the baffles as noted for, I believe, all mfgrs. EC heads in concrete tee construction. If you look at regular QR sprks and not EC, it does not appear that you need baffles. G -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Monday, October 26, 2009 5:05 PM To: [email protected] Subject: Tyco EC 14 & Double Tee's In the Design Criteria these heads are listed for the generic obstructed construction. Great, 1-6" down 22" max etc. But then there is a special application for concrete tee's that gives you up to 31" down if you meet all the other criteria. Think baffles 32' o.c. So the question is if I can hold the 22" and meet the normal obstruction rules can I use these under tee's like normal obstructed construction or do I still have to use the special application requirements? (Tyco is closed for the day) I think the answer is yes. I think the special application is only for an exception to the "exception" that allows 22" down compared to the normal 1-12". But I can read it either way. In this case I'd like to stick with 22" because I can with the particulars on the job. So I have a biased opinion. And I'm only bidding so not in a pinch (yet). Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)