Most of the time it depends on the arrangement of the evaporators in the 
freezer and rack layouts.  When the HVAC units are hung down the center you can 
most times access the walls for HSW's but if the evaps are down the sides you 
can often use dry pendants in the ceilings.   


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, October 29, 2009 4:31 AM
To: [email protected]
Subject: Re: walk in freezers


In central Puget Sound I am used to seeing dry pendant sprinklers used in 
freezers. I've seldom seen sidewalls used. 

Bruce Verhei 

----- Original Message -----
From: "Forest Wilson" <[email protected]>
To: [email protected]
Sent: Wednesday, October 28, 2009 9:09:55 PM GMT -08:00 US/Canada Pacific
Subject: Re: walk in freezers 

This came up on a recent job. 
The GC said that everyone else does it, so why can't we? 
I told them they would need to sign a waiver and obtain Building Official 
approval. 

The problem is the fact that everyone else is doing it, as you reference. They 
are setting a false standard. 

I stood my ground and won the battle with the GC. At the close of the project, 
there was a meeting with the Architect called "Lessons Learned" which all 
subcontractors were asked to attend. 
I suggested that they invest in consulting a FPE to review their plans for 
matters such as this. They replied that the jobs are bid design build for fire 
protection. 
I didn't bother explaining that the individual that prepares my shop Drawings 
is a Fire Sprinkler Layout Technician and not a Designer/PE and that most 
sprinkler companies do not employ PEs. 
If your customer would have consulted an FPE prior to bid, the PE may have said 
that we need room to run piping along the freezer. 

Pretending the problem doesn't exist is not the best solution, I would tell 
them you need room to run the pipe unless they want to pay extra for a dry 
system or antifreeze. 
Also, if you use the large K factor dry sidewalls they zany store within 36" of 
ceiling? Most owners would decline that option. 


Forest Wilson 

Project Manager
Cherokee Fire Protection Co. 
3195 Dayton Xenia Rd Ste 900
Dayton OH 45434 

ph: 937-376-2333
fx: 614-455-4324
cell: 937-307-5647 


. 



Visit our blog: www.cherokee-fire.blogspot.com 







NOTICE: The information contained in this email is intended to be solely for 
the use of the named individual or entity to which it is directed and may 
contain information that is privileged or otherwise confidential. It is not 
intended for transmission to, or receipt by, anyone other than the named 
addressee (or a person authorized to deliver it to the named addressee). It 
should not be copied or forwarded to any unauthorized persons. If you have 
received this electronic mail transmission in error, please delete it from your 
system without copying or forwarding it, and notify the sender of the error by 
reply email or by calling Cherokee Fire Protection Co. at
888-347-3079 toll free. 


-----Original Message-----
From: Jack Leadbetter <[email protected]>
To: [email protected] <[email protected]>
Cc: <[email protected]>
<[email protected]>
Sent: Wed, 28 Oct 2009 19:27:18 -0400
Subject: Re: walk in freezers 

You have to do it correctly-period! 

Sent from Jack Leadbetter's
iPhone 

On Oct 28, 2009, at 7:13 PM, "Tom Duross" <[email protected]> wrote: 

> Guilty
> 
> George Church
> 
> 
> Subject: walk in freezers
> 
> OK, honesty time here. None of the companies I worked for in the past 
> ever adhered to the 10x10 spacing rules for sidewalls in walk-in 
> freezers and coolers.
> 
> 
> 
> Is this common? I know that many times you can't feasibly put heads 
> down the side and are forced to install them in the end making the 
> coverage length well over 10'.
> 
> 
> 
> Comments? 
> 
> 
> 
> Greg McGahan
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected] (Put the word unsubscribe in the subject 
> field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 

For Technical Assistance, send an email to: [email protected] 

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 

For Technical Assistance, send an email to: [email protected] 

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to