IDK where the FPE is. We were contacted by the base and asked to just do this 
"simple" job.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Thursday, October 29, 2009 8:55 AM
To: [email protected]
Subject: RE: walk in freezers

This is probably obvious but you do know they go to a 12" deflector.  If the
condensing unit is thin enough?  Any chance of move the condensing unit to a
better location like along the wall with the sidewalls and add one
underneath for the obstruction? 

Also if this is Fed Govt where is the FPE?  I thought they were required on
all Govt work.  If there is an FPE this isn't your problem to solve.  I know
you would still try to be helpful.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, October 29, 2009 8:33 AM
To: [email protected]
Subject: RE: walk in freezers

I can put ec sidewalls, but again, they won't meet the letter of the law as
far as obstructions go.

I believe that one ss sidewall will flood that space and we would be fine,
but alas, code doesn't say that. Because these are free standing, and there
are only 2 that are adjacent, reason would dictate that only the heads in 2
coolers would ever go off at once. Calced out, we have plenty of water.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Thursday, October 29, 2009 8:29 AM
To: [email protected]
Subject: RE: walk in freezers

AF loop with EC SW?

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, October 29, 2009 8:26 AM
To: [email protected]
Subject: RE: walk in freezers

BTW, the ones I was referring to are the ones installed outside the building
with the door being on the inside the building. Hence the sidewalls. 

The reason I am asking the question in this particular case is that the
units are free standing outside and we DO know what they are storing in
them. Pendents are out of the question per the owner - Fed Govt - and the
Fire Chief is unsure of what he wants. He is trying to make a bad situation
better and we are trying to do it correctly without going overboard. 2 of
the coolers are side by side with a common wall so there is no way to put
sidewalls on opposite sides of the wall even if we wanted to. They don't
want pipe inside, EC heads will not meet the letter of the law due to the
units inside.

I was trying to get a feel for what others are seeing/doing in these cases.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to