Maybe they can get some stimulus money to hire FPEs.......

At 11:00 AM 10/29/2009, you wrote:

>Since the fed govmt is the owner, they should be more apt to accept 
>reality than a private owner.
>The Architect should have considered this before the plans and specs 
>were issued.
>I would tell them the plans lack proper design and since the specs 
>don't allow you to install piping in the freezer than the Architect 
>needs to modify his design.
>You can't do the impossible. You are in the right, so put it back in 
>the Architects lap. Maybe on the next job they will consider 
>consulting a FPE before the plans are issued.
>
>
>Forest Wilson
>
>Project Manager
>Cherokee Fire Protection Co.
>3195 Dayton Xenia Rd Ste 900
>Dayton OH 45434
>
>ph: 937-376-2333
>fx: 614-455-4324
>cell: 937-307-5647
>
>
>.
>
>
>
>Visit our blog: www.cherokee-fire.blogspot.com
>
>
>
>
>
>
>
>NOTICE: The information contained in this email is intended to be 
>solely for the use of the named individual or entity to which it is 
>directed and may contain information that is privileged or otherwise 
>confidential. It is not intended for transmission to, or receipt by, 
>anyone other than the named addressee (or a person authorized to 
>deliver it to the named addressee). It should not be copied or 
>forwarded to any unauthorized persons. If you have received this 
>electronic mail transmission in error, please delete it from your 
>system without copying or forwarding it, and notify the sender of 
>the error by reply email or by calling Cherokee Fire Protection Co. 
>at 888-347-3079 toll free.
>
>
>-----Original Message-----
>From: Greg McGahan <[email protected]>
>To: [email protected]
>Sent: Thu, Oct 29, 2009 9:32 am
>Subject: RE: walk in freezers
>
>
>
>I can put ec sidewalls, but again, they won't meet the letter of the 
>law as far
>s obstructions go.
>I believe that one ss sidewall will flood that space and we would be 
>fine, but
>las, code doesn't say that. Because these are free standing, and 
>there are only
>  that are adjacent, reason would dictate that only the heads in 2 
> coolers would
>ver go off at once. Calced out, we have plenty of water.
>Greg McGahan
>perations Manager
>Living Water Fire Protection
>160 McKenzie Road
>.O. Box 877
>antonment, Florida 32533
>850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>[email protected]
>
>----Original Message-----
>rom: [email protected] 
>[mailto:[email protected]]
>n Behalf Of Chris Cahill
>ent: Thursday, October 29, 2009 8:29 AM
>o: [email protected]
>ubject: RE: walk in freezers
>AF loop with EC SW?
>Chris Cahill, P.E.
>ire Protection Engineer
>entry Fire Protection, Inc.
>
>63-658-4483
>63-658-4921 fax
>
>mail: [email protected]
>
>ail: P.O. Box 69
>        Waverly, MN 55390
>
>ocation: 4439 Hwy 12 SW
>              Waverly, MN 55390
>----Original Message-----
>rom: [email protected]
>mailto:[email protected]] On Behalf Of Greg McGahan
>ent: Thursday, October 29, 2009 8:26 AM
>o: [email protected]
>ubject: RE: walk in freezers
>BTW, the ones I was referring to are the ones installed outside the building
>ith the door being on the inside the building. Hence the sidewalls.
>The reason I am asking the question in this particular case is that the
>nits are free standing outside and we DO know what they are storing in
>hem. Pendents are out of the question per the owner - Fed Govt - and the
>ire Chief is unsure of what he wants. He is trying to make a bad situation
>etter and we are trying to do it correctly without going overboard. 2 of
>he coolers are side by side with a common wall so there is no way to put
>idewalls on opposite sides of the wall even if we wanted to. They don't
>ant pipe inside, EC heads will not meet the letter of the law due to the
>nits inside.
>I was trying to get a feel for what others are seeing/doing in these cases.
>Greg McGahan
>perations Manager
>Living Water Fire Protection
>160 McKenzie Road
>.O. Box 877
>antonment, Florida 32533
>850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>[email protected]
>
>----Original Message-----
>rom: [email protected]
>mailto:[email protected]] On Behalf Of
>[email protected]
>ent: Thursday, October 29, 2009 7:36 AM
>o: [email protected]
>ubject: RE: walk in freezers
>Most of the time it depends on the arrangement of the evaporators in the
>reezer and rack layouts.  When the HVAC units are hung down the center you
>an most times access the walls for HSW's but if the evaps are down the
>ides you can often use dry pendants in the ceilings.
>
>raig L. Prahl, CET
>ire Protection Specialist
>echanical Department
>H2MHILL
>ockwood Greene
>500 International Drive
>O Box 491, Spartanburg, SC  29304-0491
>irect - 864.599.4102
>ax - 864.599.8439
>[email protected]
>ttp://www.ch2m.com
>
>----Original Message-----
>rom: [email protected]
>mailto:[email protected]] On Behalf Of
>[email protected]
>ent: Thursday, October 29, 2009 4:31 AM
>o: [email protected]
>ubject: Re: walk in freezers
>
>n central Puget Sound I am used to seeing dry pendant sprinklers used in
>reezers. I've seldom seen sidewalls used.
>Bruce Verhei
>----- Original Message -----
>rom: "Forest Wilson" <[email protected]>
>o: [email protected]
>ent: Wednesday, October 28, 2009 9:09:55 PM GMT -08:00 US/Canada Pacific
>ubject: Re: walk in freezers
>This came up on a recent job.
>he GC said that everyone else does it, so why can't we?
>  told them they would need to sign a waiver and obtain Building Official
>pproval.
>The problem is the fact that everyone else is doing it, as you reference.
>hey are setting a false standard.
>I stood my ground and won the battle with the GC. At the close of the
>roject, there was a meeting with the Architect called "Lessons Learned"
>hich all subcontractors were asked to attend.
>  suggested that they invest in consulting a FPE to review their plans for
>atters such as this. They replied that the jobs are bid design build for
>ire protection.
>  didn't bother explaining that the individual that prepares my shop
>rawings is a Fire Sprinkler Layout Technician and not a Designer/PE and
>hat most sprinkler companies do not employ PEs.
>f your customer would have consulted an FPE prior to bid, the PE may have
>aid that we need room to run piping along the freezer.
>Pretending the problem doesn't exist is not the best solution, I would tell
>hem you need room to run the pipe unless they want to pay extra for a dry
>ystem or antifreeze.
>lso, if you use the large K factor dry sidewalls they zany store within 36"
>f ceiling? Most owners would decline that option.
>
>orest Wilson
>Project Manager
>herokee Fire Protection Co.
>195 Dayton Xenia Rd Ste 900
>ayton OH 45434
>ph: 937-376-2333
>x: 614-455-4324
>ell: 937-307-5647
>
>
>
>Visit our blog: www.cherokee-fire.blogspot.com
>
>
>
>NOTICE: The information contained in this email is intended to be solely for
>he use of the named individual or entity to which it is directed and may
>ontain information that is privileged or otherwise confidential. It is not
>ntended for transmission to, or receipt by, anyone other than the named
>ddressee (or a person authorized to deliver it to the named addressee). It
>hould not be copied or forwarded to any unauthorized persons. If you have
>eceived this electronic mail transmission in error, please delete it from
>our system without copying or forwarding it, and notify the sender of the
>rror by reply email or by calling Cherokee Fire Protection Co. at
>88-347-3079 toll free.
>
>----Original Message-----
>rom: Jack Leadbetter <[email protected]>
>o: [email protected] <[email protected]>
>c: <[email protected]>
>[email protected]>
>ent: Wed, 28 Oct 2009 19:27:18 -0400
>ubject: Re: walk in freezers
>You have to do it correctly-period!
>Sent from Jack Leadbetter's
>Phone
>On Oct 28, 2009, at 7:13 PM, "Tom Duross" <[email protected]> wrote:
> > Guilty
>
>  George Church
>
>
>  Subject: walk in freezers
>
>  OK, honesty time here. None of the companies I worked for in the past
>  ever adhered to the 10x10 spacing rules for sidewalls in walk-in
>  freezers and coolers.
>
>
>
>  Is this common? I know that many times you can't feasibly put heads
>  down the side and are forced to install them in the end making the
>  coverage length well over 10'.
>
>
>
>  Comments?
>
>
>
>  Greg McGahan
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  For Technical Assistance, send an email to: [email protected]
>
>  To Unsubscribe, send an email to:Sprinklerforum-
>  [email protected] (Put the word unsubscribe in the subject
>  field)
>______________________________________________
>prinklerforum mailing list
>[email protected]
>ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>To Unsubscribe, send an email
>o:[email protected]
>Put the word unsubscribe in the subject field)
>
>______________________________________________
>prinklerforum mailing list
>[email protected]
>ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>To Unsubscribe, send an email to:[email protected]
>Put the word unsubscribe in the subject field)
>______________________________________________
>prinklerforum mailing list
>[email protected]
>ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>To Unsubscribe, send an email to:[email protected]
>Put the word unsubscribe in the subject field)
>______________________________________________
>prinklerforum mailing list
>[email protected]
>ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>To Unsubscribe, send an email to:[email protected]
>Put the word unsubscribe in the subject field)
>______________________________________________
>prinklerforum mailing list
>[email protected]
>ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>To Unsubscribe, send an email to:[email protected]
>Put the word unsubscribe in the subject field)
>_______________________________________________
>prinklerforum mailing list
>[email protected]
>ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>To Unsubscribe, send an email to:[email protected]
>Put the word unsubscribe in the subject field)
>______________________________________________
>prinklerforum mailing list
>[email protected]
>ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>To Unsubscribe, send an email to:[email protected]
>Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to