The interpretation here is that spaces that are under the building are neither 
porte'cocheres nor canopies.  We have a policy that any building recess 4 ft. 
or deeper requires sprinklers.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, November 10, 2009 15:03
To: [email protected]; Richardson, R
Subject: Re: Porte' Cochere

If there is a building on top of it, is it really a porte cochere?


At 05:36 PM 11/10/2009, you wrote:
>I searched the archives (briefly) and did not see this.
>
>Has it been discussed what a porte cochere is if does not project 
>out from a building? This is a drive thru that would be described as 
>a porte cochere except there is a building above it.
>
>Sprinklered or not? All non combustible and fire rated between this 
>area and the floor above.
>
>Greg McGahan
>Operations Manager
>
>Living Water Fire Protection
>1160 McKenzie Road
>P.O. Box 877
>Cantonment, Florida 32533
>(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>[email protected]
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
l>
        <[email protected]>
        <001301ca6252$2782bc00$6
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to