Typically the scenario that was described will not produce a 2-hour fire
stop detail.
But it is not difficult to restore it to such.  There are many existing UL
rated firestop
details, and I can send you some.

One solution is to restore the wall fire resistance with a fire stop detail
including
mineral wool and a smoke-&-fire-sealant.  Pack mineral wool into the annular
gap around the pipe, to a 25-33%
compression (don't worry, no one is measuring this) so that the entire
thickness,
and it is my personal opinion, as suspect as that may be, that this detail
is not
the essential one that the detail hangs upon.   Simply assure yourself the
hole
in the entire thickness of the wall is filled with mineral wool and the
mineral
wool is somewhat compacted.  This will just about restore the 2-hour FRR.
Use at minimum 4 pcf mineral wool.  As frosting on the cake of this firestop
detail,
one often puts a smoke seal.   One spreads the elastomerics smoke seal over
the mineral wool and extends the sealant  1/2-inch onto the wall and onto
the pipe.  what
type of smoke seal to use depends upon what firestop detail you are looking
at.
There are many manufacturers.



scot deal
excelsior fire