I would be very interested to see that report....as to "real world" I have been 
working in the DOE environment for the past 15 years and they are very much 
into compliance with the codes and standards without regard to cost.  So "in 
the real world" is not much of a consideration here without somebody writing a 
doctoral dissertation on the alternative method.  It can be ......well, 
interesting, we will say.

As far as survival of any rated barrier, the "nominal" hour rating is only for 
the prescribed conditions of the test in a very controlled environment.  "In 
the real world" you have varying fire loads, different fire dynamics than the 
E119 curve, construction variations in the wall/door/opening protection 
assembly, penetrations in walls that are not sealed/maintained, etc., etc., etc.


Hey, this is fun


Kevin Law, PE
Bechtel National, Inc.
Waste Treatment Project
Fire Protection Engineering
Work  (509) 371-3280
Cell    (509) 531-5715


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Friday, November 13, 2009 11:21 AM
To: [email protected]
Subject: RE: non-rated door

They ran sprinklers in the furnace for Tyco Window sprinklers.  Temps did not 
reach specified values but they deemed it passable based on the gas flow rate 
and complete combustion.  Or so I recall reading the report over 10 years ago 
now.  For some reason I think all testing is done on gas flow rates not 
necessarily temperature, but could be off on that. 

The only reason we don't have this is the cost of testing.  No sprinkler head 
company has seen a return on investment to do this testing.  Tyco saw a return 
on the window sprinklers, don't know if it was actually realized.  

P.S. this adding heads to small issues is done often enough in the real world.  
My opinion to follow - Bottom line is if the sprinklers work there is no need 
for a rated wall in nearly all cases.  If the sprinklers don't work 1 and 2 hr 
walls have high failure rates long before the actual rating.
3 and 4's do a bit better. Sometimes referred to maximum loss area wall.
To a large extent without operating sprinklers rated walls are only as good as 
the fire department is in putting the fire out.  Small dept or limited water 1 
and 2 hr are useless.  Big city FD 3's and 4's might be overkill.
But the codes don't factor this in, yet.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Law, Kevin W
Sent: Friday, November 13, 2009 12:56 PM
To: [email protected]
Subject: RE: non-rated door

One of the reasons that you don't find a listed application for water curtains 
on a fire door may be the difficulty in performing a test in accordance to NFPA 
252 to get a rated door.  I haven't talked to anyone at a lab facility, but I 
am thinking that they would be resistant to putting an array of sprinklers 
inside of their furnace while performing a burn test on a door assembly. Plus, 
I think that it would be tough to keep the furnace temperatures in line with 
the test curve with sprinklers inside of the furnace.  It seems that I have 
heard rumors of water curtains for glass wall assemblies (maybe it is more 
wishful thinking by artistic architects), but I don't have any experience with 
those things.  The only thing I have been able to find is water curtains for 
exposure and opening protection on exterior walls, not for anything inside of a 
building.  

If you have a daring AHJ and engineer you could write up a performance based 
criteria, but I wouldn't do it.  Fire doors are supposed to be a passive 
barrier.  If the sprinkler system has a problem, in spite of our best efforts 
(how many times have valves been shut, etc), then that door is going to BURN. 


Kevin Law, PE
Bechtel National, Inc.
Waste Treatment Project
Fire Protection Engineering
Work  (509) 371-3280
Cell    (509) 531-5715


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Kowkabany
Sent: Thursday, November 12, 2009 7:20 PM
To: [email protected]
Subject: RE: non-rated door

Matt,

There is no code or provision for being able to add a fire rating to walls or 
partitions by adding sprinklers on both sides, but I do wish I had a dollar for 
every time I have had an architect ask me this.  It seems like it would make 
sense, but there is no listing or precedence that I am aware of for doing this 
for walls - unlike what is in place for glazing with window sprinklers and such.

Luckily, rated doors are not that expensive.  Your contractor should just buy 
one.

Good luck,


Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
60 Ocean Boulevard, Suite 15
Atlantic Beach, FL 32233
904-652-4200 Phone
904-212-0868 Fax 

We have moved.  Please note our new address.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Thursday, November 12, 2009 4:41 PM
To: [email protected]
Subject: non-rated door

I have a case where a contractor wants to put a decorative (not fire rated) 
door into a rated hallway of a non-sprinkled building. I was hoping that there 
was some code or study that allows for a water curtain to be placed on both 
sides of the door in order to maintain the fire rating. Has anyone heard of 
anything like this?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) No virus found in this incoming 
message.
Checked by AVG - www.avg.com
Version: 8.5.425 / Virus Database: 270.14.60/2496 - Release Date: 11/12/09 
07:38:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to