One of the reasons that you don't find a listed application for water curtains 
on a fire door may be the difficulty in performing a test in accordance to NFPA 
252 to get a rated door.  I haven't talked to anyone at a lab facility, but I 
am thinking that they would be resistant to putting an array of sprinklers 
inside of their furnace while performing a burn test on a door assembly. Plus, 
I think that it would be tough to keep the furnace temperatures in line with 
the test curve with sprinklers inside of the furnace.  It seems that I have 
heard rumors of water curtains for glass wall assemblies (maybe it is more 
wishful thinking by artistic architects), but I don't have any experience with 
those things.  The only thing I have been able to find is water curtains for 
exposure and opening protection on exterior walls, not for anything inside of a 
building.  

If you have a daring AHJ and engineer you could write up a performance based 
criteria, but I wouldn't do it.  Fire doors are supposed to be a passive 
barrier.  If the sprinkler system has a problem, in spite of our best efforts 
(how many times have valves been shut, etc), then that door is going to BURN. 


Kevin Law, PE
Bechtel National, Inc.
Waste Treatment Project
Fire Protection Engineering
Work  (509) 371-3280
Cell    (509) 531-5715


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Kowkabany
Sent: Thursday, November 12, 2009 7:20 PM
To: [email protected]
Subject: RE: non-rated door

Matt,

There is no code or provision for being able to add a fire rating to walls or 
partitions by adding sprinklers on both sides, but I do wish I had a dollar for 
every time I have had an architect ask me this.  It seems like it would make 
sense, but there is no listing or precedence that I am aware of for doing this 
for walls - unlike what is in place for glazing with window sprinklers and such.

Luckily, rated doors are not that expensive.  Your contractor should just buy 
one.

Good luck,


Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
60 Ocean Boulevard, Suite 15
Atlantic Beach, FL 32233
904-652-4200 Phone
904-212-0868 Fax 

We have moved.  Please note our new address.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Thursday, November 12, 2009 4:41 PM
To: [email protected]
Subject: non-rated door

I have a case where a contractor wants to put a decorative (not fire rated) 
door into a rated hallway of a non-sprinkled building. I was hoping that there 
was some code or study that allows for a water curtain to be placed on both 
sides of the door in order to maintain the fire rating. Has anyone heard of 
anything like this?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) No virus found in this incoming 
message.
Checked by AVG - www.avg.com
Version: 8.5.425 / Virus Database: 270.14.60/2496 - Release Date: 11/12/09 
07:38:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to