I believe the general consensus the last time this was asked was that the 
requirement you quoted pertained to the hanger not the structure as specifying 
building requirements would be beyond the scope of NFPA 13.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg Lindholm
Sent: Monday, November 16, 2009 10:09 AM
To: SprinklerFORUM
Subject: Hangers

It's Monday and the brain doesn't seem to be working right.

Section 9.1.1.2 (2002) says that the the hangers shall be designed to support 
the water filled pipe plus 250#. Does the structure itself need to support that 
much, or just the hanger assembly itself.

Gregory Lindholm
Metro Fire Protection, Inc.
8693 SE 34th Ave.
Owatonna, MN 55060
507-451-9694
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to