Be careful though because out this way many of the lesser savvy AHJs are interpreting this to mean that the sprinkler contractor is responsible for proving the building will support the system and so the GCs are learning to specify that in their contracts knowing they'll get backing. Some (both GCs and AHJs) are even trying to require the sprinkler contractor to upgrade the structure if necessary. I have even seen one contract that was trying to pin the soils engineering on the sprinkler guy by requiring he verify that the dirt work, foundations and structure were adequate. Just last week a friend was contractually obligated for $16,000.00 worth of structural upgrades even though not a part of the contract because the AHJ wouldn't release the sprinkler permit until structural calcs were submitted with the plans.
On Mon, Nov 16, 2009 at 7:13 AM, <[email protected]> wrote: > I believe the general consensus the last time this was asked was that the > requirement you quoted pertained to the hanger not the structure as > specifying building requirements would be beyond the scope of NFPA 13. > > > > Craig L. Prahl, CET > Fire Protection Specialist > Mechanical Department > CH2MHILL > Lockwood Greene > 1500 International Drive > PO Box 491, Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > [email protected] > http://www.ch2m.com > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Greg Lindholm > Sent: Monday, November 16, 2009 10:09 AM > To: SprinklerFORUM > Subject: Hangers > > It's Monday and the brain doesn't seem to be working right. > > Section 9.1.1.2 (2002) says that the the hangers shall be designed to support > the water filled pipe plus 250#. Does the structure itself need to support > that much, or just the hanger assembly itself. > > Gregory Lindholm > Metro Fire Protection, Inc. > 8693 SE 34th Ave. > Owatonna, MN 55060 > 507-451-9694 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)