My point exactly on the smaller diameter of the single lateral,
typically.  But it's still prudent on the application we're discussing -
dead end, private main - to consider ALL demands, including irrigation.
To ignore them would be ... imprudent.

PEOPLE COULD DIE!  (With apologies to Mark Sornsin, industry watchdog.)

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Wednesday, December 02, 2009 2:11 PM
To: [email protected]
Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

but it has been addressed because SITE design is outside the scope of  
13R (and 13 for that matter).  13R requires you to include the  
domestic demand if you have a shared main to the individual building.   
Thats because the main is often quite small.  13 does not require  
adding the domestic due to the minimum 6 inch requirement

Roland

On Dec 2, 2009, at 1:57 PM, Ben Young wrote:

> Eric, I responded to your comment to expand on your last statement,  
> not to
> disagree with you.  I agree about the separate connection dilemma in  
> 13R vs
> 13 systems, and wonder why this has never been addressed by the code
> committees before.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4656 (20091202) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4656 (20091202) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to