Before the pump, between the backflow and the pump, and not after the
pump discharge check? I'm trying to picture what's different than a
typical set-up.

On Sat, Dec 5, 2009 at 10:09 AM, Forest Wilson <[email protected]> wrote:
> The backflow is installed on the supply side of the pump, city side.
> The sensing line is installed system side of backflow.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Saturday, December 05, 2009 1:00 PM
> To: [email protected]
> Subject: Re: pump sensing line
>
> I'm surprised that the BFP was allowed on the system side of the pump
> at all but since the sensing line is for pressure drop in the system
> having it there (and allowing it as Tom says from the TIAs) makes
> sense.
>
> On Sat, Dec 5, 2009 at 1:24 AM, Tom Duross <[email protected]> wrote:
>> There was a TIA 2 or 3 editions ago for systems with the BFP on the
>> discharge of the pump.  Between the loss through the BFP checks and the
>> hammer between the pump chv and the BFP, they allowed for moving it there.
>> It's correct and moreover better, also OK to combine them from the same
>> system tap (assuming the JP is also before the BFP).
>>
>> Tom
>>
>>
>> I saw a pump recently with the sensing line installed on the system side
> of
>> the backflow.
>> What is the reason for installing on the system, rather than the city side
>> of the backflow?
>> Am I correct that it should be on the city side?
>>
>> Forest Wilson
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to