if you were to install sensing line on city side/before the backflow,
wouldn't you need another backflow for the sensing line?


Bryan A. Dann
Dannba Design Services, LLC
Fire Sprinkler Designs
Office: (740) 363-5878
Cell: (740) 803-0967
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]]on Behalf Of Forest
Wilson
Sent: Saturday, December 05, 2009 1:09 PM
To: [email protected]
Subject: RE: pump sensing line


The backflow is installed on the supply side of the pump, city side.
The sensing line is installed system side of backflow.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Saturday, December 05, 2009 1:00 PM
To: [email protected]
Subject: Re: pump sensing line

I'm surprised that the BFP was allowed on the system side of the pump
at all but since the sensing line is for pressure drop in the system
having it there (and allowing it as Tom says from the TIAs) makes
sense.

On Sat, Dec 5, 2009 at 1:24 AM, Tom Duross <[email protected]> wrote:
> There was a TIA 2 or 3 editions ago for systems with the BFP on the
> discharge of the pump.  Between the loss through the BFP checks and the
> hammer between the pump chv and the BFP, they allowed for moving it there.
> It's correct and moreover better, also OK to combine them from the same
> system tap (assuming the JP is also before the BFP).
>
> Tom
>
>
> I saw a pump recently with the sensing line installed on the system side
of
> the backflow.
> What is the reason for installing on the system, rather than the city side
> of the backflow?
> Am I correct that it should be on the city side?
>
> Forest Wilson
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to