Check that;  it's a low suction sensing and the the primary pressure sensing 
line?   Disregard my earlier comment.  

Steve. 


Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Forest Wilson" <[email protected]>
Date: Sat, 5 Dec 2009 11:51:05 
To: <[email protected]>
Subject: RE: pump sensing line

Yes, Tom. 
It is a low suction sensing line, installed on the system side of the 
backflow. 
I thought they should be installed city/ supply side, apparently I am 
incorrect. 
I thought the sensing line would not be effective on the system side, 
because you could have the city main shut down and still show pressure on 
the system side of the backflow. 
-----Original Message----- 
From: [email protected] 
[mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Tom Duross 
Sent: Saturday, December 05, 2009 2:49 PM 
To: [email protected] 
Subject: RE: pump sensing line 
So you're saying the sensing line is on the pump suction from the backflow? 
And you were originally asking if it should be on the backflow supply from 
the street? 
Tom 
 
The backflow is installed on the supply side of the pump, city side. 
The sensing line is installed system side of backflow. 
 
I'm surprised that the BFP was allowed on the system side of the pump 
at all but since the sensing line is for pressure drop in the system 
having it there (and allowing it as Tom says from the TIAs) makes 
sense. 
> 
> I saw a pump recently with the sensing line installed on the system side 
of 
> the backflow. 
> What is the reason for installing on the system, rather than the city side 
> of the backflow? 
> Am I correct that it should be on the city side? 
> 
> Forest Wilson 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
For Technical Assistance, send an email to: [email protected] 
To Unsubscribe, send an email to:[email protected] 
(Put the word unsubscribe in the subject field) 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
For Technical Assistance, send an email to: [email protected] 
To Unsubscribe, send an email to:[email protected] 
(Put the word unsubscribe in the subject field) 
  
__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4662 (20091205)__________ 
The message was checked by ESET NOD32 Antivirus. 
http://www.eset.com <http://www.eset.com> 
  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to