Got a design criteria trivial question for some of the more experienced (PC for the old geezers, lol). A system installed in 1992 protecting Class III-A Combustible liquids in 55 gallon non-relieving drums stored 3 high was designed as a dry system and to Ordinary II (.20 / 1950). By today's standards NFPA 30 is the applicable code, I assume it was back then too? 2008 NFPA 30 is drastically different than when the system was designed back then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 (high temp) or 5000 (ordinary temp) this is for water w/o foam. My assumption is the system was designed inadequate back in 1992 just don't have the information to justify my statement. Can any of my fellow comrades help me out?
Thanks in advance. Also I hope all of you a very Merry Christmas. Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100 Ahtanum Road Yakima, WA 98903 Phone 509-248-4471 Fax 509-248-1180 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)