I've found a lot of chemical protection systems designed per NFPA 13 with no regard to any other Standard. Using the text in Chapter 5 within the various Hazards they base their design solely on the description of conditions and words such as "moderate" or "substantial".
Protection of chemicals is in almost all cases beyond the scope of NFPA 13 alone. You need MSDS information as we've stated here on many occasions but if you're not comfortable in analyzing chemical properties, compatibilities, extinguishing methodology (other than water), then defer to someone with the expertise. What can be especially tricky is when various types of chemicals are stored in the same area. The questions I'd be asking are how much of this chemical is present, (there are code limitations), in what kind of area does this storage exist, (dedicated chemical storage room/control area or out in the open plant area), naturally ask for MSDS, you need to know whether it's a polar solvent or hydrocarbon based material, miscibility, etc., etc., etc. In some cases a dry system may not be acceptable and you may have to go to non or single interlocked preaction instead. Lots of variables and lots of codes issues to look at in these cases. ****And by the way I don't qualify as one of the old geezers, but I have stayed in a Holiday Inn Express on more than one occasion. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jim Johnston Sent: Thursday, December 17, 2009 12:42 PM To: [email protected] Subject: Class III-A Combustible Liquids Got a design criteria trivial question for some of the more experienced (PC for the old geezers, lol). A system installed in 1992 protecting Class III-A Combustible liquids in 55 gallon non-relieving drums stored 3 high was designed as a dry system and to Ordinary II (.20 / 1950). By today's standards NFPA 30 is the applicable code, I assume it was back then too? 2008 NFPA 30 is drastically different than when the system was designed back then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 (high temp) or 5000 (ordinary temp) this is for water w/o foam. My assumption is the system was designed inadequate back in 1992 just don't have the information to justify my statement. Can any of my fellow comrades help me out? Thanks in advance. Also I hope all of you a very Merry Christmas. Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100 Ahtanum Road Yakima, WA 98903 Phone 509-248-4471 Fax 509-248-1180 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)