OH II, no, don't think so.  Plus you may have issues with extinguishment based 
on water alone since it's SG=.91 and is insoluble.  

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Thursday, December 17, 2009 3:07 PM
To: [email protected]
Subject: RE: Class III-A Combustible Liquids

Craig,
 The liquid is spearmint oil flash point 143 F, the oil is stored in 
non-relieving steel drums.  I have looked at the MSDS sheets and 2008 NFPA 30 
as well as a small section of NFPA 30 - 1993.  I am pretty comfortable with 
requirements of 1993 and 2008 just don't have the backing of what the 
requirements prior to 1993 were?  I just don't see it as Ordinary II?

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Thursday, December 17, 2009 11:20 AM
To: [email protected]
Subject: RE: Class III-A Combustible Liquids

I've found a lot of chemical protection systems designed per NFPA 13 with no 
regard to any other Standard.  Using the text in Chapter 5 within the various 
Hazards they base their design solely on the description of
conditions and words such as "moderate" or "substantial".   

Protection of chemicals is in almost all cases beyond the scope of NFPA 13 
alone.  You need MSDS information as we've stated here on many occasions but if 
you're not comfortable in analyzing chemical properties, compatibilities, 
extinguishing methodology (other than water), then defer to someone with the 
expertise.  

What can be especially tricky is when various types of chemicals are stored in 
the same area.  


The questions I'd be asking are how much of this chemical is present, (there 
are code limitations), in what kind of area does this storage exist, (dedicated 
chemical storage room/control area or out in the open plant area), naturally 
ask for MSDS, you need to know whether it's a polar solvent or hydrocarbon 
based material, miscibility, etc., etc., etc.  In some cases a dry system may 
not be acceptable and you may have to go to non or single interlocked preaction 
instead.  Lots of variables and lots of codes issues to look at in these cases.




****And by the way I don't qualify as one of the old geezers, but I have stayed 
in a Holiday Inn Express on more than one occasion.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Thursday, December 17, 2009 12:42 PM
To: [email protected]
Subject: Class III-A Combustible Liquids

Got a design criteria trivial question for some of the more experienced (PC for 
the old geezers, lol).  A system installed in 1992 protecting Class III-A 
Combustible liquids in 55 gallon non-relieving drums stored 3 high was designed 
as a dry system and to Ordinary II (.20 / 1950).  By today's standards NFPA 30 
is the applicable code, I assume it was back then too?
2008 NFPA 30 is drastically different than when the system was designed back 
then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 (high
temp) or 5000 (ordinary temp) this is for water w/o foam.  My assumption is the 
system was designed inadequate back in 1992 just don't have the information to 
justify my statement.  Can any of my fellow comrades help me out?

 

Thanks in advance.

 

Also I hope all of you a very Merry Christmas.

 

Jim Johnston, P.E.

Fire Protection Engineer

Inland Fire Protection, Inc

1100 Ahtanum Road

Yakima, WA 98903

Phone 509-248-4471

Fax 509-248-1180

[email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to