Was the building originally designed for the drum storage? Almost 
sounds like it was supposed to house something else.


At 05:21 PM 12/17/2009, you wrote:
>Unfortunately the person who designed this did it as Ord II and the AHJ
>bought off on it.  I am pretty certain the codes never allowed this hazard
>as Ord II, I just wanted to have some backing since I don't anything (NFPA
>30) prior to 1993.  Nothing like trying to solve someone else's mistake.
>
>Jim Johnston, P.E.
>Fire Protection Engineer
>Inland Fire Protection, Inc
>1100 Ahtanum Road
>Yakima, WA 98903
>Phone 509-248-4471
>Fax 509-248-1180
>[email protected]
>
>
>-----Original Message-----
>From: [email protected] [mailto:[email protected]]
>Sent: Thursday, December 17, 2009 12:25 PM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>OH II, no, don't think so.  Plus you may have issues with extinguishment
>based on water alone since it's SG=.91 and is insoluble.
>
>
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Jim Johnston
>Sent: Thursday, December 17, 2009 3:07 PM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>Craig,
>  The liquid is spearmint oil flash point 143 F, the oil is stored in
>non-relieving steel drums.  I have looked at the MSDS sheets and 2008 NFPA
>30 as well as a small section of NFPA 30 - 1993.  I am pretty comfortable
>with requirements of 1993 and 2008 just don't have the backing of what the
>requirements prior to 1993 were?  I just don't see it as Ordinary II?
>
>Jim Johnston, P.E.
>Fire Protection Engineer
>Inland Fire Protection, Inc
>1100 Ahtanum Road
>Yakima, WA 98903
>Phone 509-248-4471
>Fax 509-248-1180
>[email protected]
>
>
>-----Original Message-----
>From: [email protected] [mailto:[email protected]]
>Sent: Thursday, December 17, 2009 11:20 AM
>To: [email protected]
>Subject: RE: Class III-A Combustible Liquids
>
>I've found a lot of chemical protection systems designed per NFPA 13 with no
>regard to any other Standard.  Using the text in Chapter 5 within the
>various Hazards they base their design solely on the description of
>conditions and words such as "moderate" or "substantial".
>
>Protection of chemicals is in almost all cases beyond the scope of NFPA 13
>alone.  You need MSDS information as we've stated here on many occasions but
>if you're not comfortable in analyzing chemical properties, compatibilities,
>extinguishing methodology (other than water), then defer to someone with the
>expertise.
>
>What can be especially tricky is when various types of chemicals are stored
>in the same area.
>
>
>The questions I'd be asking are how much of this chemical is present, (there
>are code limitations), in what kind of area does this storage exist,
>(dedicated chemical storage room/control area or out in the open plant
>area), naturally ask for MSDS, you need to know whether it's a polar solvent
>or hydrocarbon based material, miscibility, etc., etc., etc.  In some cases
>a dry system may not be acceptable and you may have to go to non or single
>interlocked preaction instead.  Lots of variables and lots of codes issues
>to look at in these cases.
>
>
>
>
>****And by the way I don't qualify as one of the old geezers, but I have
>stayed in a Holiday Inn Express on more than one occasion.
>
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Jim Johnston
>Sent: Thursday, December 17, 2009 12:42 PM
>To: [email protected]
>Subject: Class III-A Combustible Liquids
>
>Got a design criteria trivial question for some of the more experienced (PC
>for the old geezers, lol).  A system installed in 1992 protecting Class
>III-A Combustible liquids in 55 gallon non-relieving drums stored 3 high was
>designed as a dry system and to Ordinary II (.20 / 1950).  By today's
>standards NFPA 30 is the applicable code, I assume it was back then too?
>2008 NFPA 30 is drastically different than when the system was designed back
>then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 (high
>temp) or 5000 (ordinary temp) this is for water w/o foam.  My assumption is
>the system was designed inadequate back in 1992 just don't have the
>information to justify my statement.  Can any of my fellow comrades help me
>out?
>
>
>
>Thanks in advance.
>
>
>
>Also I hope all of you a very Merry Christmas.
>
>
>
>Jim Johnston, P.E.
>
>Fire Protection Engineer
>
>Inland Fire Protection, Inc
>
>1100 Ahtanum Road
>
>Yakima, WA 98903
>
>Phone 509-248-4471
>
>Fax 509-248-1180
>
>[email protected]
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to