Was the building originally designed for the drum storage? Almost sounds like it was supposed to house something else.
At 05:21 PM 12/17/2009, you wrote: >Unfortunately the person who designed this did it as Ord II and the AHJ >bought off on it. I am pretty certain the codes never allowed this hazard >as Ord II, I just wanted to have some backing since I don't anything (NFPA >30) prior to 1993. Nothing like trying to solve someone else's mistake. > >Jim Johnston, P.E. >Fire Protection Engineer >Inland Fire Protection, Inc >1100 Ahtanum Road >Yakima, WA 98903 >Phone 509-248-4471 >Fax 509-248-1180 >[email protected] > > >-----Original Message----- >From: [email protected] [mailto:[email protected]] >Sent: Thursday, December 17, 2009 12:25 PM >To: [email protected] >Subject: RE: Class III-A Combustible Liquids > >OH II, no, don't think so. Plus you may have issues with extinguishment >based on water alone since it's SG=.91 and is insoluble. > > > > >Craig L. Prahl, CET >Fire Protection Specialist >Mechanical Department >CH2MHILL >Lockwood Greene >1500 International Drive >PO Box 491, Spartanburg, SC 29304-0491 >Direct - 864.599.4102 >Fax - 864.599.8439 >[email protected] >http://www.ch2m.com > > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Jim Johnston >Sent: Thursday, December 17, 2009 3:07 PM >To: [email protected] >Subject: RE: Class III-A Combustible Liquids > >Craig, > The liquid is spearmint oil flash point 143 F, the oil is stored in >non-relieving steel drums. I have looked at the MSDS sheets and 2008 NFPA >30 as well as a small section of NFPA 30 - 1993. I am pretty comfortable >with requirements of 1993 and 2008 just don't have the backing of what the >requirements prior to 1993 were? I just don't see it as Ordinary II? > >Jim Johnston, P.E. >Fire Protection Engineer >Inland Fire Protection, Inc >1100 Ahtanum Road >Yakima, WA 98903 >Phone 509-248-4471 >Fax 509-248-1180 >[email protected] > > >-----Original Message----- >From: [email protected] [mailto:[email protected]] >Sent: Thursday, December 17, 2009 11:20 AM >To: [email protected] >Subject: RE: Class III-A Combustible Liquids > >I've found a lot of chemical protection systems designed per NFPA 13 with no >regard to any other Standard. Using the text in Chapter 5 within the >various Hazards they base their design solely on the description of >conditions and words such as "moderate" or "substantial". > >Protection of chemicals is in almost all cases beyond the scope of NFPA 13 >alone. You need MSDS information as we've stated here on many occasions but >if you're not comfortable in analyzing chemical properties, compatibilities, >extinguishing methodology (other than water), then defer to someone with the >expertise. > >What can be especially tricky is when various types of chemicals are stored >in the same area. > > >The questions I'd be asking are how much of this chemical is present, (there >are code limitations), in what kind of area does this storage exist, >(dedicated chemical storage room/control area or out in the open plant >area), naturally ask for MSDS, you need to know whether it's a polar solvent >or hydrocarbon based material, miscibility, etc., etc., etc. In some cases >a dry system may not be acceptable and you may have to go to non or single >interlocked preaction instead. Lots of variables and lots of codes issues >to look at in these cases. > > > > >****And by the way I don't qualify as one of the old geezers, but I have >stayed in a Holiday Inn Express on more than one occasion. > > > >Craig L. Prahl, CET >Fire Protection Specialist >Mechanical Department >CH2MHILL >Lockwood Greene >1500 International Drive >PO Box 491, Spartanburg, SC 29304-0491 >Direct - 864.599.4102 >Fax - 864.599.8439 >[email protected] >http://www.ch2m.com > > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Jim Johnston >Sent: Thursday, December 17, 2009 12:42 PM >To: [email protected] >Subject: Class III-A Combustible Liquids > >Got a design criteria trivial question for some of the more experienced (PC >for the old geezers, lol). A system installed in 1992 protecting Class >III-A Combustible liquids in 55 gallon non-relieving drums stored 3 high was >designed as a dry system and to Ordinary II (.20 / 1950). By today's >standards NFPA 30 is the applicable code, I assume it was back then too? >2008 NFPA 30 is drastically different than when the system was designed back >then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 (high >temp) or 5000 (ordinary temp) this is for water w/o foam. My assumption is >the system was designed inadequate back in 1992 just don't have the >information to justify my statement. Can any of my fellow comrades help me >out? > > > >Thanks in advance. > > > >Also I hope all of you a very Merry Christmas. > > > >Jim Johnston, P.E. > >Fire Protection Engineer > >Inland Fire Protection, Inc > >1100 Ahtanum Road > >Yakima, WA 98903 > >Phone 509-248-4471 > >Fax 509-248-1180 > >[email protected] > > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)