Craig,
 The liquid is spearmint oil flash point 143 F, the oil is stored in
non-relieving steel drums.  I have looked at the MSDS sheets and 2008 NFPA
30 as well as a small section of NFPA 30 - 1993.  I am pretty comfortable
with requirements of 1993 and 2008 just don't have the backing of what the
requirements prior to 1993 were?  I just don't see it as Ordinary II?

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Thursday, December 17, 2009 11:20 AM
To: [email protected]
Subject: RE: Class III-A Combustible Liquids

I've found a lot of chemical protection systems designed per NFPA 13 with no
regard to any other Standard.  Using the text in Chapter 5 within the
various Hazards they base their design solely on the description of
conditions and words such as "moderate" or "substantial".   

Protection of chemicals is in almost all cases beyond the scope of NFPA 13
alone.  You need MSDS information as we've stated here on many occasions but
if you're not comfortable in analyzing chemical properties, compatibilities,
extinguishing methodology (other than water), then defer to someone with the
expertise.  

What can be especially tricky is when various types of chemicals are stored
in the same area.  


The questions I'd be asking are how much of this chemical is present, (there
are code limitations), in what kind of area does this storage exist,
(dedicated chemical storage room/control area or out in the open plant
area), naturally ask for MSDS, you need to know whether it's a polar solvent
or hydrocarbon based material, miscibility, etc., etc., etc.  In some cases
a dry system may not be acceptable and you may have to go to non or single
interlocked preaction instead.  Lots of variables and lots of codes issues
to look at in these cases.




****And by the way I don't qualify as one of the old geezers, but I have
stayed in a Holiday Inn Express on more than one occasion.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Thursday, December 17, 2009 12:42 PM
To: [email protected]
Subject: Class III-A Combustible Liquids

Got a design criteria trivial question for some of the more experienced (PC
for the old geezers, lol).  A system installed in 1992 protecting Class
III-A Combustible liquids in 55 gallon non-relieving drums stored 3 high was
designed as a dry system and to Ordinary II (.20 / 1950).  By today's
standards NFPA 30 is the applicable code, I assume it was back then too?
2008 NFPA 30 is drastically different than when the system was designed back
then, I have some stuff out of 1993 NFPA 30 that says .25 over 3000 (high
temp) or 5000 (ordinary temp) this is for water w/o foam.  My assumption is
the system was designed inadequate back in 1992 just don't have the
information to justify my statement.  Can any of my fellow comrades help me
out?

 

Thanks in advance.

 

Also I hope all of you a very Merry Christmas.

 

Jim Johnston, P.E.

Fire Protection Engineer

Inland Fire Protection, Inc

1100 Ahtanum Road

Yakima, WA 98903

Phone 509-248-4471

Fax 509-248-1180

[email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to