--- On Thu, 12/31/09, David Blackwell <[email protected]> wrote:

From: David Blackwell <[email protected]>
Subject: RE: 13R: Fuel Fired Equipment
To: [email protected]
Date: Thursday, December 31, 2009, 7:33 PM

2007 NFPA 13R 6.9.6 does state that "Sprinklers shall not be required in
attics..." but note that if you read it all the way through all the
example areas to the end example it also adds the caveat at the end
"...and other concealed spaces that are not used or intended for living
purposes or storage and do not contain fuel-fired equipment."

Roland answered this question for AFSA found on the Internet at: 
http://www.mail-archive.com/[email protected]/msg00079.ht
ml

in the following technical update:



----------------------------------

TECHNICAL UPDATE

FEBRUARY 4, 2009

----------------------------------



"Does the presence of the fuel fired equipment (gas fired water heaters)
in an otherwise unused attic as referenced in NFPA 13R, Section 6.9.6
require the attic to be designed and calculated for other than light
hazard occupancy?" 



We have reviewed NFPA 13R, 2007 Edition that you indicated as the
applicable standard. Our informal interpretation is that the attic space
will have to be protected to the spacing and hydraulic design criteria
of NFPA 13 for Light Hazard Occupancies. 



NFPA 13R Section 6.9.6 will require the protection of attics that
contain fuel-fired equipment. The design criteria for the attic are set
by 6.8.2.1 that directs you to NFPA 13 and it states, "For areas outside
the dwelling unit, the design discharge and design area criteria shall
comply with NFPA 13, Standard for the Installation of Sprinkler Systems,
unless permitted by 6.8.2.2 and 6.8.2.3." This clarifies that the
requirement for the protection of the attic will have to be to NFPA 13
requirements. The area will have to be designed to light hazard
occupancy if it does not meet any of the allowances of NFPA 13R, Section
6.8.2.2 and will have to be a minimum of 1500 sq. ft with a density of
..10 gpm/sq. ft. Regular mechanical rooms in NFPA 13 occupancy with
gas-fired equipment are typically ordinary hazard occupancy. Two primary
reasons are that the equipment is typically large and we expect the
owner to use the space for storage and collected combustibles.
Mechanical rooms without gas-fired equipment typically get kicked into
an ordinary hazard classification for the later reason. In this case of
water heaters in an attic, not only are the units small, it does not add
to the fuel load but it is an ignition source. Thus, the definition for
light hazard "where quantity and/or combustibility of contents is low"
does apply. 



-----------------

Technical Update is prepared by the Technical Services Dept. of the
AFSA: Vice President of Engineering and Technical Services Roland
Huggins, a PE registered in fire protection engineering; Phill Brown, a
NICET IV certified automatic sprinkler technician and NFPA Certified
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire
protection engineering technologist. This is provided with the
understanding that the AFSA assumes no liability for this opinion or
actions taken on it and they are not to be considered the official
position of the NFPA or its technical committees. 



Copyright (c) 2009, American Fire Sprinkler Association. All Rights
Reserved 

--------------------------

 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ralphy
Henderson
Sent: Thursday, December 31, 2009 1:28 PM
To: [email protected]
Subject: 13R: Fuel Fired Equipment

Hello all,

NFPA #13R does not require the sprinkling of concealed combustible
spaces except for when a few conditions exist one of them being when
fuel fired equipment is located there. I have a project with wood open
web trusses with a drop ceiling. Gas furnaces are located above the grid
clg. Does this mean I have to sprinkle the entire attic or can I just
put some localized coverage near the units? I didn't see anything in 'R'
or the commentary that addresses this specifically.

Thanks,

RH






      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to