Also if you're on IBC to use 13R some separations must be extended to the
roof. (Corridor walls, and unit walls)Not interior unit walls from baths
closets or the like. 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David
Blackwell
Sent: Thursday, December 31, 2009 12:34 PM
To: [email protected]
Subject: RE: 13R: Fuel Fired Equipment

2007 NFPA 13R 6.9.6 does state that "Sprinklers shall not be required in
attics..." but note that if you read it all the way through all the example
areas to the end example it also adds the caveat at the end "...and other
concealed spaces that are not used or intended for living purposes or
storage and do not contain fuel-fired equipment."

Roland answered this question for AFSA found on the Internet at: 
http://www.mail-archive.com/[email protected]/msg00079.ht
ml

in the following technical update:



----------------------------------

TECHNICAL UPDATE

FEBRUARY 4, 2009

----------------------------------



"Does the presence of the fuel fired equipment (gas fired water heaters) in
an otherwise unused attic as referenced in NFPA 13R, Section 6.9.6 require
the attic to be designed and calculated for other than light hazard
occupancy?" 



We have reviewed NFPA 13R, 2007 Edition that you indicated as the applicable
standard. Our informal interpretation is that the attic space will have to
be protected to the spacing and hydraulic design criteria of NFPA 13 for
Light Hazard Occupancies. 



NFPA 13R Section 6.9.6 will require the protection of attics that contain
fuel-fired equipment. The design criteria for the attic are set by 6.8.2.1
that directs you to NFPA 13 and it states, "For areas outside the dwelling
unit, the design discharge and design area criteria shall comply with NFPA
13, Standard for the Installation of Sprinkler Systems, unless permitted by
6.8.2.2 and 6.8.2.3." This clarifies that the requirement for the protection
of the attic will have to be to NFPA 13 requirements. The area will have to
be designed to light hazard occupancy if it does not meet any of the
allowances of NFPA 13R, Section
6.8.2.2 and will have to be a minimum of 1500 sq. ft with a density of .10
gpm/sq. ft. Regular mechanical rooms in NFPA 13 occupancy with gas-fired
equipment are typically ordinary hazard occupancy. Two primary reasons are
that the equipment is typically large and we expect the owner to use the
space for storage and collected combustibles.
Mechanical rooms without gas-fired equipment typically get kicked into an
ordinary hazard classification for the later reason. In this case of water
heaters in an attic, not only are the units small, it does not add to the
fuel load but it is an ignition source. Thus, the definition for light
hazard "where quantity and/or combustibility of contents is low"
does apply. 



-----------------

Technical Update is prepared by the Technical Services Dept. of the
AFSA: Vice President of Engineering and Technical Services Roland Huggins, a
PE registered in fire protection engineering; Phill Brown, a NICET IV
certified automatic sprinkler technician and NFPA Certified Fire Protection
Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering
technologist. This is provided with the understanding that the AFSA assumes
no liability for this opinion or actions taken on it and they are not to be
considered the official position of the NFPA or its technical committees. 



Copyright (c) 2009, American Fire Sprinkler Association. All Rights Reserved


--------------------------

 

David W. S. Blackwell, II, PE, CFI-I, CFPE Engineering
----------------------------------------------------------------
Office of State Fire Marshal
141 Monticello Trail
Columbia, SC 29203
Phone:  803.896.9833
Fax:  803.896.9806
Email:  [email protected]
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp
---------------------------------------------------------------- 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ralphy
Henderson
Sent: Thursday, December 31, 2009 1:28 PM
To: [email protected]
Subject: 13R: Fuel Fired Equipment

Hello all,

NFPA #13R does not require the sprinkling of concealed combustible spaces
except for when a few conditions exist one of them being when fuel fired
equipment is located there. I have a project with wood open web trusses with
a drop ceiling. Gas furnaces are located above the grid clg. Does this mean
I have to sprinkle the entire attic or can I just put some localized
coverage near the units? I didn't see anything in 'R'
or the commentary that addresses this specifically.

Thanks,

RH






      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to