Spot on- and why we have prescriptive codes to apply- you did- he nneds to
understand you comply and that's it, absent clear and present danger,
contractual obligations...

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Monday, February 08, 2010 6:38 PM
To: [email protected]
Subject: RE: Beam obstruction rules

Let me guess:  he doesn't have an issue with sprinkler spray obstruction,
but has an issue with heat flow getting to the sprinkler.  Assuming that's
the case, he may (or may not) have a point - your beams are 15" deep and
heat would more likely flow parallel to the beams rather than cross under
the beam & fuse the sprinkler.  To my knowledge, 13 doesn't address that.
Unless someone wants to do some fire modeling, it's all opinion and theory.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Cliff Whitfield
> Sent: Monday, February 08, 2010 4:02 PM
> To: [email protected]
> Subject: RE: Beam obstruction rules
> 
> Todd,
> 
> There are no lights or fans or ducts that would create an issue.  The
> deflector is 6" below the deck so I only have 9" to worry about.  I'm
> trying
> to not say exactly what this guy has said so that I can get other
> opinions
> before I influence anyone's answer.
> 
> If anyone else wants to throw in their two cents, that would be great.
> 
> Thanks,
> Cliff
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd
> Williams
> Sent: Monday, February 08, 2010 3:59 PM
> To: [email protected]
> Subject: Re: Beam obstruction rules
> 
> How far down is the deflector from the deck? Any lights/ceiling fans
> that could be in the way?
> 
> 
> At 04:39 PM 2/8/2010, you wrote:
> >Forum,
> >
> >I have a question regarding beam obstruction rules for standard spray
> >uprights.
> >
> >I have a light hazard project that has 15" deep beams.  The first beam
> is
> 9'
> >from the wall and the next beam is 17' away from beam #1.  If I space
> my
> >first head 5' away from beam #1 so that it is not an obstruction (per
> table
> >8.6.5.1.2-NFPA 13, 2007 ed), can my next head be 15' from head #1?
> This is
> >not supposed to be a trick question but I have a disagreement with an
> FPE
> on
> >this.
> >
> >Thanks for your insight on this one.
> >
> >Cliff Whitfield, SET
> >President
> >Fire Design, Inc.
> >
> >[email protected]
> >www.fire-design.com
> >
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________