Fire tests conducted by TYCO and the Mattress industry showed no delay in
fire spread, because all of the mattresses are wrapped in poly to keep them
clean until they are sold, and the exposed poly burns really good. At that
point the covering can't and doesn't slow down the fire spread. Stored in
racks on edge in less than 2 min. the hoses had to be brought out, because
the .45 Gpm/sf (density a guess from memory) wasn't doing it. After the test
TYCO suggested that rather than lower the design density they would have to
consider raising it.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, February 08, 2010 3:16 PM
To: [email protected]
Subject: RE: L'il Abner-Mattress Tester

The covering was intended to help prevent fires from exposure to direct
ignition sources like cigarettes.  Polyurethane foam degrades at around 600F
and the flashpoint of the foam is still somewhere near or slightly above
200F so the fire resistant covering isn't going to change the combustion
properties of the underlying foam material.  So from a fire scenario
standpoint, it's an unknown just what delay the covering would really have
against fire.  But heat is heat, when the fire gets to a certain
temperature, the foam is going to either ignite or the pile collapse.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, February 08, 2010 4:01 PM
To: [email protected]
Subject: L'il Abner-Mattress Tester

Back in 2007 the CPSC required a fire-resistant outer (fabric) shell on all
mattresses and box springs for sale in the USA.

Is anyone familiar with this to be able to tell if this reduces the
hazardous classification of the foam when stored in a retail store stockroom
to 12' high? Stored on floor, flat, as if prepared for a princess and a pea.

Owner would prefer not to take .2/1500 to .6 for obvious reasons, one being
tenant fitout of a portion of an existing retail center.

George Church
Rowe Sprinkler 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to