Remember the building code is the document that tells you when and where 
systems are required.  If a jurisdiction is using NFPA 101 as their building 
code then of course that would govern the decision.  But if you are under the 
ICC, UFC, SBC codes or similar, they take precedence on what you can and cannot 
do as far as omitting sprinklers.

Typically unless you're dealing with a special hazard type of situation, water 
based sprinklers have an excellant track record of performace.  


Craig Prahl
________________________________________
From: [email protected] 
[[email protected]] On Behalf Of Ing. Donato Pirro 
[[email protected]]
Sent: Thursday, February 11, 2010 3:54 PM
To: [email protected]
Subject: RE: Gas systems replacing sprinklers

Aaron,  check NFPA 101-09 section 9.7.3 (Other Automatic Extinguishing
Equipment). I believe the intent is to permit an automatic extinguishing
system other than water sprinklers to substitute for a NFPA 13 sprinkler
system ONLY where automatic sprinklers are not able to control a such fire
(an example could be the protection of water reactive chemicals).

Where an automatic sprinkler system is capable of controlling the fuel that
will burn, the automatic sprinkler system must be present. Also please note
that clean agent systems relay on a fixed quantity of gas to extinguish the
fire. If doors are left open so as to dilute gas concentration, there is no
back-up for extinguishing the fire. That is why the automatic sprinkler
system is needed in all rooms where a code requires protection throughout.

D.Pirro


-----Mensaje original-----
De: [email protected]
[mailto:[email protected]] En nombre de Rod DiBona
Enviado el: Martes, 09 de Febrero de 2010 05:50 p.m.
Para: [email protected]
Asunto: RE: Gas systems replacing sprinklers

Thanks Joe. Good info. I never considered that the ability to take the
increases would be jeopardized when the clean agent is approved as an
alternative...

Rod
Rapid Fire

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joe Burtell
Sent: Tuesday, February 09, 2010 3:33 PM
To: [email protected]
Subject: RE: Gas systems replacing sprinklers

Here is what our local fire marshal got back from the ICC
Subject: IFC 904.2 question
Hi Scott,

I have a question for you.

Section 904.2 states that "Automatic fire-extinguishing systems shall not be
considered alternatives for the purposes of exceptions or reductions allowed
by other requirements of this code."

Does this mean that if I have a building that is fully protected with
sprinklers but one room in the building contains an alternate (clean agent)
system for protection of computers instead of sprinklers, no exceptions or
reductions in code are allowed for whole building? Or does it only apply to
a situation where the designer wants to install an alternate system
throughout the entire building instead of sprinklers?

Thanks for any help you can provide.

Mike

Mike

Both answers are correct. If you have a building sprinklered throughout in
accordance with NFPA 13, and sprinklers are removed from a room that is not
exempted by Section 903.3.1.1.1, then you technically cannot take advantage
of all of the credits allowed by the IBC and IFC. If a building requires
automatic sprinklers but the designer chooses a clean agent system, these
same credits cannot be taken.

Alternative fire extinguishing systems have a limited amount of agent and
are generally designed for a single application onto a particular hazard
versus automatic sprinklers which can protect a variety of hazards for a
given occupancy hazard and generally has a greater amount of agent (e.g.,
water) that is available.

Scott Stookey
Senior Technical Staff - Product Development
International Code Council (ICC)
807 Sweetwater River Drive
Austin, Texas 78748-2238
Office: 1-888-422-7233 (ICC-SAFE) X 3473 (FIRE)
Cellular: 512-716-9595
[email protected]
www.iccsafe.org




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to