I would think the use of the pull station is more a question than its definition. If the pull station is located in the area of operation of the PA system and is used as a manual release, as long as there is still an automatic release I.E. smoke/heat detectors, and all are wired to the listed release panel, OK. If however the pull station is one of the many required throughout the facility, any one of which activates the alarm system, then it is defiantly not a "Release" device it is an "Initiating" device. Even if that initiates a release panel to open the deluge valve.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Forest Wilson Sent: Wednesday, February 24, 2010 9:32 AM To: [email protected] Subject: RE: pull stations I would suspect the problem is the EOR may be telling the sprinkler contractor it is his scope of work, not the alarm contractor scope of work. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, February 24, 2010 11:22 AM To: [email protected] Subject: RE: pull stations Ok, so is there a problem with his definition? By NFPA 72 definition a pull station is an initiating device. Its actuation initiates a response. So in the case of the preaction system it is an initiating device since it initiates opening of the PA valve. Whatever it's called, whether it be pull station or releasing device is pretty much irrelevant. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Wednesday, February 24, 2010 11:03 AM To: [email protected] Subject: pull stations Got an engineer telling me that a "pull station" wired to a non-interlock pre-action system is NOT an alarm device and is part of the sprinkler system per NFPA #13. He is calling it a releasing device and not a "pull station" by definition. ???thoughts? Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)