I would think the use of the pull station is more a question than its
definition.
If the pull station is located in the area of operation of the PA system and
is used as a manual release, as long as there is still an automatic release
I.E. smoke/heat detectors, and all are wired to the listed release panel,
OK.
If however the pull station is one of the many required throughout the
facility, any one of which activates the alarm system, then it is defiantly
not a "Release" device it is an "Initiating" device. Even if that initiates
a release panel to open the deluge valve.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest Wilson
Sent: Wednesday, February 24, 2010 9:32 AM
To: [email protected]
Subject: RE: pull stations

I would suspect the problem is the EOR may be telling the sprinkler
contractor it is his scope of work, not the alarm contractor scope of work.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, February 24, 2010 11:22 AM
To: [email protected]
Subject: RE: pull stations

Ok, so is there a problem with his definition?   By NFPA 72 definition a
pull station is an initiating device.  Its actuation initiates a response.
So in the case of the preaction system it is an initiating device since it
initiates opening of the PA valve.

Whatever it's called, whether it be pull station or releasing device is
pretty much irrelevant. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Wednesday, February 24, 2010 11:03 AM
To: [email protected]
Subject: pull stations

Got an engineer telling me that a "pull station" wired to a non-interlock
pre-action system is NOT an alarm device and is part of the sprinkler system
per NFPA #13. He is calling it a releasing device and not a "pull station"
by definition.

???thoughts?

Greg McGahan

Living Water Fire Protection
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to