No, that would be too simple.... I am the contractor and the EOR is saying it in is in our scope of work, no big deal. The issue is that he didn't want the "releasing devices" tied into the alarm system and wanted them installed in accordance with NFPA #13. The "RD" specified by the AHJ to be electric (this is the AHJ's brainchild/requirement) and that it should electrically release the solenoid on the Preaction valve. He said NFPA #72 doesn't apply to the "RD's".
I said no way. BTW, the AHJ said no way as well. He wants the "Pull Stations" monitored for integrity, so if there is a bad wire, etc they get a trouble signal. Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Forest Wilson Sent: Wednesday, February 24, 2010 10:32 AM To: [email protected] Subject: RE: pull stations I would suspect the problem is the EOR may be telling the sprinkler contractor it is his scope of work, not the alarm contractor scope of work. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, February 24, 2010 11:22 AM To: [email protected] Subject: RE: pull stations Ok, so is there a problem with his definition? By NFPA 72 definition a pull station is an initiating device. Its actuation initiates a response. So in the case of the preaction system it is an initiating device since it initiates opening of the PA valve. Whatever it's called, whether it be pull station or releasing device is pretty much irrelevant. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Wednesday, February 24, 2010 11:03 AM To: [email protected] Subject: pull stations Got an engineer telling me that a "pull station" wired to a non-interlock pre-action system is NOT an alarm device and is part of the sprinkler system per NFPA #13. He is calling it a releasing device and not a "pull station" by definition. ???thoughts? Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)