No, that would be too simple.... I am the contractor and the EOR is saying it 
in is in our scope of work, no big deal. The issue is that he didn't want the 
"releasing devices" tied into the alarm system and wanted them installed in 
accordance with NFPA #13.  The "RD" specified by the AHJ to be electric (this 
is the AHJ's brainchild/requirement) and that it should electrically release 
the solenoid on the Preaction valve. He said NFPA #72 doesn't apply to the 
"RD's".

I said no way. BTW, the AHJ said no way as well. He wants the "Pull Stations" 
monitored for integrity, so if there is a bad wire, etc they get a trouble 
signal.

Greg McGahan

Living Water Fire Protection
 (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Forest Wilson
Sent: Wednesday, February 24, 2010 10:32 AM
To: [email protected]
Subject: RE: pull stations

I would suspect the problem is the EOR may be telling the sprinkler
contractor it is his scope of work, not the alarm contractor scope of work.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, February 24, 2010 11:22 AM
To: [email protected]
Subject: RE: pull stations

Ok, so is there a problem with his definition?   By NFPA 72 definition a
pull station is an initiating device.  Its actuation initiates a response.
So in the case of the preaction system it is an initiating device since it
initiates opening of the PA valve.

Whatever it's called, whether it be pull station or releasing device is
pretty much irrelevant. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Wednesday, February 24, 2010 11:03 AM
To: [email protected]
Subject: pull stations

Got an engineer telling me that a "pull station" wired to a non-interlock
pre-action system is NOT an alarm device and is part of the sprinkler system
per NFPA #13. He is calling it a releasing device and not a "pull station"
by definition.

???thoughts?

Greg McGahan

Living Water Fire Protection
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to