Greg,
You got to living in wishful thinking world today. You are outdoors.
8'0". I see nothing to suggest otherwise unless you want to say your
soffit is not an open process building ("...such as in open process
structures...." I don't think this example is intended to be
exclusive) it's pretty definitive.
On Tue, Mar 16, 2010 at 7:12 AM, Greg McGahan <[email protected]> wrote:
> NFPA #15 6.5.2.4
>
> Para .2 - Pilot lines under a ceiling - spacing per 13
> Para .8 - Outdoors - spacing at 8'-0
>
> Situation - Soffit on the exterior of a building 2'-4" wide.......
>
> Which one is the absolute in this situation?
>
> Greg McGahan
>
> Living Water Fire Protection
> (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
>