We are replacing all of the existing 5.6k nozzles (10'-0 on center) with 11.2's 
spaced at 8' on center. We are replacing all of the pipe feeding the existing 
nozzles but had hoped to reuse the existing pilot lines to save the owner money.

I asked NFPA, but like I said, I don't have an answer.

Greg McGahan

Living Water Fire Protection
 (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, March 16, 2010 10:52 AM
To: [email protected]
Subject: RE: pilot lines

Exposure protection has different rules than protection under an overhang due 
to width.  Different purpose, different criteria.  Spacing of the nozzles is 
dependant on overlap and wetting of the complete surface moreso than NFPA 13 
general spacing requirements.  Spacing of the sensing devices (pilot heads) is 
based on the outdoor spacing rules as has been discussed.  If your installation 
meets the 15ft height criteria from ground to soffit as stated in 6.5.2.4.9 and 
there no levels above to be protected then I see no reason why you can't 
increase the pilot spacing to 10ft. as noted.

Are you having to do anything with the discharge nozzles or is the problem just 
in the pilot head spacing?  Knowing what the spacing and discharge angles of 
the discharge nozzles is critical.  Also at what angle are they in relation to 
the adjacent wall?  

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, March 16, 2010 11:36 AM
To: [email protected]
Subject: RE: pilot lines

Ok, let me clarify. This is exposure protection against the side of a building 
per 13 and 15. There is a soffit at the roof level about 3' deep and a little 
over 2' wide. So this is not an exposure protection system with dry pilot heads 
in the complete open with nothing to collect heat.

With that being said, I am fine with the 8' if that is indeed the intent of 15 
and there is no argument from me.

Before I have that answer conclusively though, it seems that the requirement 
for 8' spacing in the great wide open then it should be increased by some 
measure if there is collection. My line of reasoning follows the thought that 
if this were a normal closed head system protecting under the soffit, then the 
heads would be spaced at a max of 15'.


Greg McGahan

Living Water Fire Protection
 (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, March 16, 2010 10:26 AM
To: [email protected]
Subject: RE: pilot lines

All pilot heads are the intermediate type like used in racks.  Para. 6.5.2.4.9 
has very specific wording, can your installation meet that criteria?  If you 
can meet the vertical spacing and arrangement requirements then you can apply 
.9, if you can't then you're back to para. ....8 

Since there is less structure to trap heat on typical outdoor arrangements, the 
spacing is reduced to 8ft. horizontally and also vertical separation 
limitations between levels must be recognized.





Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, March 16, 2010 10:23 AM
To: [email protected]
Subject: RE: pilot lines

What about Para .9 that allows you to increase the spacing to 10'-0" for a 
given level? This para's explanation is indicative of pilot heads with nothing 
above them to collect heat.

I also sent this to NFPA.

Greg McGahan

Living Water Fire Protection
 (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, March 16, 2010 9:19 AM
To: [email protected]
Subject: RE: pilot lines

If it's outside - 8ft.  It's either inside or outside. 

Is this for a deluge system?


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, March 16, 2010 10:12 AM
To: [email protected]
Subject: pilot lines

NFPA #15 6.5.2.4

Para .2 - Pilot lines under a ceiling - spacing per 13 Para .8 - Outdoors - 
spacing at 8'-0

Situation - Soffit on the exterior of a building 2'-4" wide.......

Which one is the absolute in this situation?

Greg McGahan

Living Water Fire Protection
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to