Well, I'm happy to be wrong here. I'd rather it was you making money
because some misanthrope screwed up than you being said misanthrope.

On Tue, Mar 16, 2010 at 12:50 PM, George Church <[email protected]> wrote:
> I suppose the pilot lines are 1/2" galv 40 so you can't make it real ez by
> drilling in a snap halfway between the existing 12' oc and end up with 6'
> spacing very economically? Unscrew a pilot head, install a 1/2" tee,
> re-install, and stab 1/2" pipe 6' over to a new intermediate? Either f these
> would be less than ripping it out and starting over, I'd think- but YOU'RE
> looking at it.
>
> glc
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg McGahan
> Sent: Tuesday, March 16, 2010 11:56 AM
> To: [email protected]
> Subject: RE: pilot lines
>
> We are replacing all of the existing 5.6k nozzles (10'-0 on center) with
> 11.2's spaced at 8' on center. We are replacing all of the pipe feeding the
> existing nozzles but had hoped to reuse the existing pilot lines to save the
> owner money.
>
> I asked NFPA, but like I said, I don't have an answer.
>
> Greg McGahan
>
> Living Water Fire Protection
>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Tuesday, March 16, 2010 10:52 AM
> To: [email protected]
> Subject: RE: pilot lines
>
> Exposure protection has different rules than protection under an overhang
> due to width.  Different purpose, different criteria.  Spacing of the
> nozzles is dependant on overlap and wetting of the complete surface moreso
> than NFPA 13 general spacing requirements.  Spacing of the sensing devices
> (pilot heads) is based on the outdoor spacing rules as has been discussed.
> If your installation meets the 15ft height criteria from ground to soffit as
> stated in 6.5.2.4.9 and there no levels above to be protected then I see no
> reason why you can't increase the pilot spacing to 10ft. as noted.
>
> Are you having to do anything with the discharge nozzles or is the problem
> just in the pilot head spacing?  Knowing what the spacing and discharge
> angles of the discharge nozzles is critical.  Also at what angle are they in
> relation to the adjacent wall?
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg McGahan
> Sent: Tuesday, March 16, 2010 11:36 AM
> To: [email protected]
> Subject: RE: pilot lines
>
> Ok, let me clarify. This is exposure protection against the side of a
> building per 13 and 15. There is a soffit at the roof level about 3' deep
> and a little over 2' wide. So this is not an exposure protection system with
> dry pilot heads in the complete open with nothing to collect heat.
>
> With that being said, I am fine with the 8' if that is indeed the intent of
> 15 and there is no argument from me.
>
> Before I have that answer conclusively though, it seems that the requirement
> for 8' spacing in the great wide open then it should be increased by some
> measure if there is collection. My line of reasoning follows the thought
> that if this were a normal closed head system protecting under the soffit,
> then the heads would be spaced at a max of 15'.
>
>
> Greg McGahan
>
> Living Water Fire Protection
>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Tuesday, March 16, 2010 10:26 AM
> To: [email protected]
> Subject: RE: pilot lines
>
> All pilot heads are the intermediate type like used in racks.  Para.
> 6.5.2.4.9 has very specific wording, can your installation meet that
> criteria?  If you can meet the vertical spacing and arrangement requirements
> then you can apply .9, if you can't then you're back to para. ....8
>
> Since there is less structure to trap heat on typical outdoor arrangements,
> the spacing is reduced to 8ft. horizontally and also vertical separation
> limitations between levels must be recognized.
>
>
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg McGahan
> Sent: Tuesday, March 16, 2010 10:23 AM
> To: [email protected]
> Subject: RE: pilot lines
>
> What about Para .9 that allows you to increase the spacing to 10'-0" for a
> given level? This para's explanation is indicative of pilot heads with
> nothing above them to collect heat.
>
> I also sent this to NFPA.
>
> Greg McGahan
>
> Living Water Fire Protection
>  (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Tuesday, March 16, 2010 9:19 AM
> To: [email protected]
> Subject: RE: pilot lines
>
> If it's outside - 8ft.  It's either inside or outside.
>
> Is this for a deluge system?
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg McGahan
> Sent: Tuesday, March 16, 2010 10:12 AM
> To: [email protected]
> Subject: pilot lines
>
> NFPA #15 6.5.2.4
>
> Para .2 - Pilot lines under a ceiling - spacing per 13 Para .8 - Outdoors -
> spacing at 8'-0
>
> Situation - Soffit on the exterior of a building 2'-4" wide.......
>
> Which one is the absolute in this situation?
>
> Greg McGahan
>
> Living Water Fire Protection
> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to