We have a situation that has been talked about in the past but I can't
remember what was resolved.
Back to back sprinkler heads in a double 2X4 fire rated wall.  The
exception in the IBC 712.3.2 #3
deals with membrane penetrations and sprinkler escutcheon.  What happens
when you have 
a through penetration such as B/B sprinklers?  There is no exception in
section 712.3.1 of the IBC
for sprinkler escutcheons in through penetrations and the manufacture
states that you cannot fire caulk
a sprinkler escutcheon.  Would we need to use the donk style sprinkler
esch and fire caulk around the pipe?
 
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
<http://www.designbuildfire.com/> 