Normally that is what I would do but in this case there is a 1" air gap
between the 2x4 walls.
5/8" rock,2x4 stud wall,1" air gap, 2x4 stud wall,5/8" rock with
insulation in the stud cavities. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
McMahon
Sent: Wednesday, March 17, 2010 12:46 PM
To: [email protected]
Subject: RE: Through wall penetration with sprinkler heads

True if the heads are truly Back to Back, we have overcome this with
Bld.
Official approval by offsetting the heads one joist space so the stud
forms the fire blocking.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Wednesday, March 17, 2010 11:42 AM
To: '[email protected]'
Subject: RE: Through wall penetration with sprinkler heads

Membrane penetrations only apply when penetrating only one side of the
assembly, see definition in ch. 7.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research
Services National Institutes of Health
301-496-0487

-----Original Message-----
From: Thom McMahon [mailto:[email protected]]
Sent: Wednesday, March 17, 2010 1:28 PM
To: [email protected]
Subject: RE: Through wall penetration with sprinkler heads

712.4.1.2 Membrane penetrations. Penetrations of membranes that are part
of a fire-resistance-rated horizontal assembly shall comply with Section
712.4.1.1.1 or 712.4.1.1.2. Where floor/ceiling assemblies are required
to have a minimum 1-hour fire-resistance rating, recessed fixtures shall
be installed such that the required fire resistance will not be reduced.
Exceptions:
4. The annular space created by the penetration of a fire sprinkler,
provided it is covered by a metal escutcheon plate.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, March 17, 2010 11:13 AM
To: [email protected]
Subject: Through wall penetration with sprinkler heads

We have a situation that has been talked about in the past but I can't
remember what was resolved.
Back to back sprinkler heads in a double 2X4 fire rated wall.  The
exception in the IBC 712.3.2 #3 deals with membrane penetrations and
sprinkler escutcheon.  What happens when you have a through penetration
such as B/B sprinklers?  There is no exception in section 712.3.1 of the
IBC for sprinkler escutcheons in through penetrations and the
manufacture states that you cannot fire caulk a sprinkler escutcheon.
Would we need to use the donk style sprinkler esch and fire caulk around
the pipe?
 
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
<http://www.designbuildfire.com/>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to