712.4.1.2 Membrane penetrations. Penetrations of
membranes that are part of a fire-resistance-rated horizontal
assembly shall comply with Section 712.4.1.1.1
or 712.4.1.1.2. Where floor/ceiling assemblies are
required to have a minimum 1-hour fire-resistance rating,
recessed fixtures shall be installed such that the
required fire resistance will not be reduced.
Exceptions:
4. The annular space created by the penetration of
a fire sprinkler, provided it is covered by a
metal escutcheon plate.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, March 17, 2010 11:13 AM
To: [email protected]
Subject: Through wall penetration with sprinkler heads

We have a situation that has been talked about in the past but I can't
remember what was resolved.
Back to back sprinkler heads in a double 2X4 fire rated wall.  The
exception in the IBC 712.3.2 #3
deals with membrane penetrations and sprinkler escutcheon.  What happens
when you have 
a through penetration such as B/B sprinklers?  There is no exception in
section 712.3.1 of the IBC
for sprinkler escutcheons in through penetrations and the manufacture
states that you cannot fire caulk
a sprinkler escutcheon.  Would we need to use the donk style sprinkler
esch and fire caulk around the pipe?
 
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
<http://www.designbuildfire.com/> 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to