Membrane penetrations only apply when penetrating only one side of the 
assembly, see definition in ch. 7.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

-----Original Message-----
From: Thom McMahon [mailto:[email protected]] 
Sent: Wednesday, March 17, 2010 1:28 PM
To: [email protected]
Subject: RE: Through wall penetration with sprinkler heads

712.4.1.2 Membrane penetrations. Penetrations of
membranes that are part of a fire-resistance-rated horizontal
assembly shall comply with Section 712.4.1.1.1
or 712.4.1.1.2. Where floor/ceiling assemblies are
required to have a minimum 1-hour fire-resistance rating,
recessed fixtures shall be installed such that the
required fire resistance will not be reduced.
Exceptions:
4. The annular space created by the penetration of
a fire sprinkler, provided it is covered by a
metal escutcheon plate.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, March 17, 2010 11:13 AM
To: [email protected]
Subject: Through wall penetration with sprinkler heads

We have a situation that has been talked about in the past but I can't
remember what was resolved.
Back to back sprinkler heads in a double 2X4 fire rated wall.  The
exception in the IBC 712.3.2 #3
deals with membrane penetrations and sprinkler escutcheon.  What happens
when you have 
a through penetration such as B/B sprinklers?  There is no exception in
section 712.3.1 of the IBC
for sprinkler escutcheons in through penetrations and the manufacture
states that you cannot fire caulk
a sprinkler escutcheon.  Would we need to use the donk style sprinkler
esch and fire caulk around the pipe?
 
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
<http://www.designbuildfire.com/> 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to