Something I've always wondered..
On a combination system, we take the hose demand at the fdv on the riser for
the floor we're calculating but I used to have a couple of firefighters who
worked part time for me.  They always told me they connected a floor or two
below (or above) to keep a separation before entering the fire floor.  I
often wondered why we didn't calc. it that way.
Tom

Right- but you'd take the 150 off at the nearest hydrant to pump suction.
And you could leave the 100 inside off there, too, if there aren't inside
hose connections.