10' of 4" or 6" standpipe, not real significant. If you're that close in
your calc, it'd be scary.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, April 07, 2010 9:10 AM
To: [email protected]
Subject: RE: Hose allowance digress

Tom,

Typically that's how its taught, connect to the hose valve on the floor
below the fire, stretch the line up the stairwell to the floor above the
fire and back down to the fire floor with the nozzle ending up at the
fire floor stairway door.  The idea being to avoid clutter on the fire
floor and let gravity do some of the work feeding the hose line from
above rather than having to pull it up from below. That doesn't mean its
done that way everywhere, but what I've described is the norm. 

So does stretching the line one flight above the fire floor and two
floors above the connected hose valve effect anything ?  Hmmm

John Drucker
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom
Duross
Sent: Wednesday, April 07, 2010 8:04 AM
To: [email protected]
Subject: RE: Hose allowance digress

Something I've always wondered..
On a combination system, we take the hose demand at the fdv on the riser
for the floor we're calculating but I used to have a couple of
firefighters who worked part time for me.  They always told me they
connected a floor or two below (or above) to keep a separation before
entering the fire floor.  I often wondered why we didn't calc. it that
way.
Tom

Right- but you'd take the 150 off at the nearest hydrant to pump
suction.
And you could leave the 100 inside off there, too, if there aren't
inside hose connections.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity
to which it is addressed and may contain information that is privileged and
confidential, nor is it, unless specifically stated, intended to be relied
upon by any person or persons other than the individual or entity named
above and no warranties or representations are made or intended to persons
or entities not named above.  If the reader is not the intended recipient,
you are hereby notified that any dissemination, distribution or copying of
this communication is strictly prohibited.  If you have received this
communication in error, please notify us immediately by telephone, return
this message to the address above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to