Thank you Ken , couldn't agree more.

 
---- Chuck Hollands <[email protected]> wrote: 
> Amen and thank gosh for people like Ken Wagoner!
> 
> Kind Regards,
> Chuck Hollands
> Millennium Fire protection Corporation
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> ParsleyConsulting
> Sent: Wednesday, May 19, 2010 8:36 AM
> To: [email protected]
> Subject: Re: 13R sprinklers
> 
> Chris,
> 
> I'll can tell you exactly where the SOB-PE is wrong.  Consider a 16' x 
> 16' room.  How many residential sprinklers?
> 
> In the world of the listing criteria from Tyco, or any other 
> manufacturer, this room requires a single sprinkler, absent anything 
> that would prevent it not exceeding 10' from a wall.
> 
> In the world of the PE who Todd is dealing with, the answer is no, you 
> must install four sprinklers, because your coverage cannot exceed 12' x 
> 12', or 6'-0" from any wall.  He has quadrupled the number of sprinklers 
> in the room, and I might add, quadrupled the cost of the sprinkler 
> system to the customer.  And this will hold true in every room in the 
> building which is greater than 12'x12' in size. 
> 
> Here's another part of that consideration.  The same aforementioned 
> 16'x16' room, would require the hydraulic calculations to prove that 
> 13.0 gpm would be delivered to the single sprinkler in the room, if the 
> listing criteria and NFPA-13D were followed.  In the world of the PE, 
> that changes again, and now Todd has to prove that 26 gpm can be 
> provided in the same room, all because the engineer doesn't accept the 
> testing and listing data from the manufacturer, and has chosen to ignore 
> the black and white text of the applicable standard. 
> 
> Now throw in the possible addition of 5 gpm for a domestic flow, which 
> many AHJ's are requiring, and now you're potentially flowing more than 
> 31 gpm through the meter.  Depending on the manufacturer this might rule 
> out the use of a 3/4" meter and force the homeowner into purchasing an 
> upgraded meter, at a cost of thousands of dollars.  Steve Leyton can 
> give you more information on that than I can, but in one water district 
> here in San Diego county the difference in a 3/4" vs. a 1" water meter 
> is $14,000. 
> 
> Four times the sprinklers the listing would require, larger pipe than is 
> necessary, an upgraded meter, and potentially a pump.  What if the 
> system were supplied from onsite storage?  Now the tank must be twice 
> the size as well.
> 
> Doesn't add up to a "better" approach to residential fire protection 
> from where I sit.
> 
> He's spending four times the owners money necessary [not his own, mind 
> you] to provide the same level of fire protection.  Not "better", the 
> same.  At four times the cost.
> 
>  From perspective of this quite humble sprinkler layout technician 
> that's just wrong.
> -- 
> PARSLEY CONSULTING
> Ken Wagoner, SET
> 760.745.6181 voice
> 760.745.0537 fax
> [email protected] <mailto:[email protected]> e-mail
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> 
> 
> 
> 
> 
> Chris Cahill wrote:
> > This is important - LET ME PLAY DEVIL'S ADVOCATE, where is the engineer
> > WRONG?  Quick look at Tyco LF II 4.9 pendant 12' x 12' is 13 gpm.  And at
> 18
> > gpm it's a 13.49 psi start.  The sidewalls at 4.2 will do 13gpm at 9.2 psi
> > so you are not forced under a 7 psi start. So he won't let you use 16' x
> 20'
> > spacing?  Just because one won't allow what in essence is extended
> coverage
> > doesn't make one ignorant. 
> >
> > Is this not the equivalent of not allowing sched 7 and only allowing sched
> > 40 threaded noting sched 7 has many more times the CRR?  Both cases are
> text
> > book verse a real application.  Perhaps some think 12' x 12' spacing is
> > better then EC and 40 is better than 7 when applied to a real project.
> How
> > often do we see a spec say no EC? How often do we see no reduction for QR?
> >
> > I acknowledge you did say he is reading out of the where not been listed
> > with special...so his argument may be flawed but his conclusion probably
> > isn't from his perspective.  I'm sure you recall the 13/18 was the
> original
> > NFPA 13R/D spec and the first heads had no other spacing options.  But it
> > also looks like at least in Tyco's case the low end it's the same on the
> > 13gpm side.  Yeah the dual gpm is gone.  But an engineer can spec any
> > density greater than the minimum.     
> >
> > I didn't talk with the engineer perhaps he/she/it is ignorant or perhaps
> > just exercising engineering prerogative like all the other times we see
> it.
> >
> >
> > Again that was the other side of the coin.  I'M ON YOUR SIDE TODD.  I
> > wouldn't cost the owner extra money in what will probably be a lot of
> extra
> > heads but I don't see anything WRONG here. 
> >
> > Chris Cahill, P.E.
> > Fire Protection Engineer
> > Sentry Fire Protection, Inc.
> >  
> > 763-658-4483
> > 763-658-4921 fax
> >  
> > Email: [email protected]
> >  
> > Mail: P.O. Box 69
> >         Waverly, MN 55390
> >  
> > Location: 4439 Hwy 12 SW
> >               Waverly, MN 55390
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > [email protected]
> > Sent: Wednesday, May 19, 2010 8:39 AM
> > To: [email protected]
> > Subject: RE: 13R sprinklers
> >
> > Todd ,
> >  Are you saying the engineer has seen and has read these sections of 13R
> and
> > still doesn't understand the requirements ? If so , you may have to go
> over
> > his head to a higher authority or say a prayer and try to appease him as
> > best you can.
> >
> > Good Luck ,
> >
> > Lamar Vaughn , SET
> >
> >   
> > ---- Todd Williams <[email protected]> wrote: 
> >   
> >> Discharge - 6.7.1.1.1, Coverage - 6.7.1.3.1. NFPA 13R (2002)
> >>
> >>
> >>
> >> At 08:23 AM 5/19/2010, you wrote:
> >>     
> >>> I'd ask him to please, for your edification, cite the sections of 
> >>> the NFPA Standard where he derived his specification data.
> >>>
> >>> I guess he was looking at sprinkler data sheets and when it didn't 
> >>> say that the sprinkler is designed for 0.10 or whatever gpm/sq. ft 
> >>> he thinks it falls into that category?
> >>>
> >>>
> >>> Craig L. Prahl, CET
> >>> Fire Protection Specialist
> >>> Mechanical Department
> >>> CH2MHILL
> >>> Lockwood Greene
> >>> 1500 International Drive
> >>> Spartanburg, SC  29304-0491
> >>> Direct - 864.599.4102
> >>> Fax - 864.599.8439
> >>> [email protected]
> >>> http://www.ch2m.com
> >>>
> >>> -----Original Message-----
> >>> From: [email protected] 
> >>> [mailto:[email protected]] On Behalf Of Todd
> >>>       
> > Williams
> >   
> >>> Sent: Wednesday, May 19, 2010 6:11 AM
> >>> To: [email protected]
> >>> Subject: 13R sprinklers
> >>>
> >>> I am working on a project with a rather ignorant engineer who will
> >>> not accept listed flow requirements for residential sprinklers. He is
> >>> insisting on using the 12 x 12 spacing, 13 gpm for multiple sprinkler
> >>> flow and 18 for single sprinkler flow (we have to calculate both). My
> >>> question may be one of semantics, but this is what the engineer is
> >>> hanging everything on. Both the above spacing and discharge
> >>> requirements are under sections entitled "Sprinklers That Have Not
> >>> Been Listed with Specific (Discharge/Coverage) Criteria". Since
> >>> virtually all of the residential sprinklers I am aware of have
> >>> specific design and coverage criteria, am I to assume based on the
> >>> wording that sprinklers with specific criteria cannot be used under
> >>> this section? If so, are there any sprinklers without specific
> >>> criteria currently on the market?
> >>>
> >>> Todd G. Williams, PE
> >>> Fire Protection Design/Consulting
> >>> Stonington, CT
> >>> 860.535.2080
> >>> www.fpdc.com
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to: [email protected]
> >>>
> >>> To Unsubscribe, send an email
> to:[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to: [email protected]
> >>>
> >>> To Unsubscribe, send an email
> to:[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>>       
> >> Todd G. Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, CT
> >> 860.535.2080
> >> www.fpdc.com
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email to:[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>     
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> >   
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to