3/4 is allowed in non-ferrous materials.

Jamie
Sent from my iPhone

On Jun 14, 2010, at 4:07 PM, James Zimmerman <[email protected]> wrote:

> I have a specification that states nothing less than 1" pipe shall  
> be used
> for a sprinkler system. Is there anywhere in NFPA 13 that prohibits  
> the use
> of 3/4" pipe? I know in the 2007 Edition 8.15.19 states new  
> installations
> shall have a minimum of 1" outlets for piping supplying sprinklers  
> below
> ceilings. This section doesn't specifically come out and state that  
> all
> piping must be 1". In 8.15.19.4 all piping with the exception of a  
> 4" nipple
> shall be 1" minimum.
> Am I missing something or is 3/4" allowed per NFPA 13?
>
> Thanks,
>
> Jim