NFPA 13 does not allow smaller than 1" steel pipe (except in a specific 
situation for retrofit).  For copper and CPVC, NFPA 13 permits ¾" pipe.

On 6/14/2010 1:07 PM, James Zimmerman wrote:
> I have a specification that states nothing less than 1" pipe shall be used
> for a sprinkler system. Is there anywhere in NFPA 13 that prohibits the use
> of 3/4" pipe? I know in the 2007 Edition 8.15.19 states new installations
> shall have a minimum of 1" outlets for piping supplying sprinklers below
> ceilings. This section doesn't specifically come out and state that all
> piping must be 1". In 8.15.19.4 all piping with the exception of a 4" nipple
> shall be 1" minimum.
> Am I missing something or is 3/4" allowed per NFPA 13?
>