Be careful if it is seismic. -----Original Message----- From: James Zimmerman [mailto:[email protected]] Sent: Monday, June 14, 2010 3:07 PM To: [email protected] Subject: 3/4" pipe
I have a specification that states nothing less than 1" pipe shall be used for a sprinkler system. Is there anywhere in NFPA 13 that prohibits the use of 3/4" pipe? I know in the 2007 Edition 8.15.19 states new installations shall have a minimum of 1" outlets for piping supplying sprinklers below ceilings. This section doesn't specifically come out and state that all piping must be 1". In 8.15.19.4 all piping with the exception of a 4" nipple shall be 1" minimum. Am I missing something or is 3/4" allowed per NFPA 13? Thanks, Jim _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)