Thanks, that is what I was over looking. Saw the pipe schedule stuff but
missed 22.4.1.2

On Mon, Jun 14, 2010 at 3:34 PM, John Drucker <[email protected]>wrote:

> 2007 NFPA-13
>
> 22.4.1.2 Hydraulically Calculated - Pipe sizes shall be no less than 1 in.
> (25 mm) nominal for ferrous piping and 3⁄4 in. (20 mm) nominal for copper
> tubing or nonmetallic piping listed for fire sprinkler service.
>
> Table 22.5.2.2.1 Light Hazard Pipe Schedules - 1" Min
>
> Table 22.5.3.4 Ordinary Hazard Pipe Schedule = 1" Min
>
> Table 9.2.2.1(a) Maximum Distance Between Hangers (ft-in.)- 3/4 - Steel -
> Not Allowed (N/A)
>
> Hope that helps
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of James Zimmerman
> Sent: Monday, June 14, 2010 4:07 PM
> To: [email protected]
> Subject: 3/4" pipe
>
> I have a specification that states nothing less than 1" pipe shall be used
> for a sprinkler system. Is there anywhere in NFPA 13 that prohibits the use
> of 3/4" pipe? I know in the 2007 Edition 8.15.19 states new installations
> shall have a minimum of 1" outlets for piping supplying sprinklers below
> ceilings. This section doesn't specifically come out and state that all
> piping must be 1". In 8.15.19.4 all piping with the exception of a 4"
> nipple
> shall be 1" minimum.
> Am I missing something or is 3/4" allowed per NFPA 13?
>
> Thanks,
>
> Jim
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to