Agreed, the IBC per chapter 411 of the 2009 code volume does address
this standard for Special Amusement.  Keep in mind the occupant load of
less than 50 dictates how this occupancy is referenced and classified.
Less than 50 shall comply with the requirement for a group B (business)
occupancy.  In my experience,  past occupancy load calcs on these type
uses total greater than 50.  So I maintain the Assembly use.

Eric Wiseman
Town of Wake Forest Inspections
(919) 435-9526

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ben Young
Sent: Tuesday, July 13, 2010 5:01 PM
To: [email protected]
Subject: Re: Haunted House

Did the IBC not pick up BOCA's special amusement building occupancy?  As
Eric said, I would guess Assembly.
The last haunted house I was involved in was from 2002.

Benjamin Young



On Tue, Jul 13, 2010 at 4:52 PM, Autry, David
<[email protected]>wrote:

> What occupancy would you give to a haunted house?
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
>
> ** Note new email address: [email protected]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3ASprinklerforum-request@
firesprinkler.org>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 



Correspondence to and from this E-mail address may be subject to the North 
Carolina Public Records Law (NCGS Chapter 132) and may be disclosed to third 
parties.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to