That's what two great instructors said in RI!

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487


-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Wednesday, October 06, 2010 12:27 PM
To: Roland Huggins; [email protected]
Subject: Re: Backflow Forward Flow Test

This should be added to the ug and oh acceptance certificates in 13  

Forest Wilson
Cherokee Fire

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Roland Huggins" <[email protected]>
Date: Wed, Oct 6, 2010 11:30 am
Subject: Backflow Forward Flow Test
To: <[email protected]>

NFPA 13 says to be flow tested at SYSTEM DEMAND.  One might want to  
use the definition that system demand is Sprinkler flow plus hose  
demand but the INTENT is to only add hose demand if there are hose  
connections (or a hydrant) downstream.  NFPA 25 is much more precise  
in their description and says exactly that.

There is guidance in the annex regarding what can be used but NFPA 13  
is very sloppy regarding this issue.  There will be discussion this  
cycle regarding adding to the list of things required for the  
submittal verification that the provided means is capable of meeting  
the system demand.

Roland

On Oct 4, 2010, at 11:45 AM, Ron Greenman wrote:

> As we discussed a few weeks ago the first thing we need to know is  
> what do we need to test: forward flow only, forward flow at the  
> hydraulic design, at the design plus hose stream, at the capacity of  
> the lead-in at the supply pressure, to insure that the checks  
> completely open...? That will determine what size feed you need to  
> your test point. Then how do you demonstrate you've met the test  
> parameters? Barring an answer to the first question you can't answer  
> the second so this is a mute discussion that is based on reading  
> chicken bones for a solution. The question isn't how to perform a  
> forward flow test but rather what question am I trying to answer  
> when doing so. How will then obvious.
>
> Ron Greenman
> ...On the phone

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to