NFPA 13, 8.6.2.1.2 If it meets the small room criteria - "The protection area of coverage for each sprinkler in the small room shall be the area of the room divided by the number of sprinklers in each room."
SHARON ALVES Senior Fire Sprinkler Designer LP Consulting Engineers, Inc. Mechanical - Electrical - Plumbing Engineers - Fire Protection 1075 Creekside Ridge Drive, Suite 175 Roseville, CA 95678 P: 916.771.0778 - F: 916.783.9446 [email protected] This email and its attachments are the sole property of LP Consulting Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2010. This communication with its contents may contain confidential and/or legally privileged information. It is solely for the use of the intended recipient(s). Unauthorized interception, review, use or disclosure is prohibited and may violate applicable laws including the Electronic Communications Privacy Act. If you are not the intended recipient, please contact the sender and destroy all copies of the communication. The sender and its company do not guarantee that this email or its attachments is free of viruses nor does it accept any liability for same _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)