Ask the engineer, really the only one that can answer.

Chris

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cliff
Whitfield
Sent: Wednesday, November 10, 2010 4:59 PM
To: [email protected]
Subject: Seismic Question

 I have an unusual situation on a project and would like some opinions.

We are currently doing a project where seismic bracing has been specified
for 'blast protection' (or something like that).  The project is not in a
zone that would otherwise require seismic protection.  So here is my
question.

Are restraining straps required to be installed on the beam clamps?  

Now before you answer, consider this - NFPA 13 2007 - 9.3.7.1 - C-type
clamps ... used to attach hangers to the building structure IN AREAS SUBJECT
TO EARTHQUAKES shall be equipped with a retraining strap.

Ok, now what is your opinion?

Thanks,

Cliff Whitfield, SET
President
Fire Design, Inc.