Interesting.  Unless I'm misreading something, NFPA 20 and the IBC/IFC
flat-out contradict each other on this issue.  The IBC/IFC says they have to
be electrically supervised, sealed or locked.  NFPA 20 (2010) says they need
nothing.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of John Drucker
> Sent: Thursday, December 02, 2010 8:29 PM
> To: [email protected]
> Subject: RE: tamper switches
> 
> Ed,
> 
> Heres the references from the I-Codes
> 
> 2006 and 2009 IBC/IFC
> 
> [F] 903.4 Sprinkler system supervision and alarms.
> 
> All valves controlling the water supply for automatic sprinkler systems,
> pumps, tanks, water levels and temperatures, critical air pressures and
> waterflow switches on all sprinkler systems shall be electrically
> supervised
> [by a listed fire alarm control unit][Added 2009].
> 
> Exceptions:
> 
> 4. Jockey pump control valves that are sealed or locked in the open
> position.
> 
> Hope that helps
> 
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
> 
> Not the official position of any agency, association, committee or
> otherwise. Verify all applications and approvals with your local
> authority
> having jurisdiction.
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ed Kramer
> Sent: Thursday, December 02, 2010 6:03 PM
> To: [email protected]
> Subject: RE: tamper switches
> 
> Thanks, Greg.  Looks like it's time to update my NFPA 20.
> 
> > -----Original Message-----
> > From: [email protected] [mailto:sprinklerforum-
> > [email protected]] On Behalf Of Greg McGahan
> > Sent: Thursday, December 02, 2010 3:40 PM
> > To: [email protected]
> > Subject: Re: tamper switches
> >
> > *4.25.5.7*  2010 edition  - the JP Isolation valves are NOT required
> to
> > be supervised.
> >
> >
> > On 12/2/2010 3:48 PM, Ed Kramer wrote:
> > > Are suction and discharge valves of a jockey pump required to be
> > supervised?
> > > Section 5.16.1 (NFPA 20 2007) says 'yes', but doesn't clarify if its
> > > intended to apply to both fire pumps and jockey pumps.  Anybody want
> > to
> > > speculate on the intent?  I've always put tamper switches on them,
> but
> > now
> > > I'm wondering if it's required or not.
> > >
> > >
> > >
> > > Ed Kramer
> > >
> > > Littleton, CO
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > For Technical Assistance, send an email to:
> [email protected]
> > >
> > > To Unsubscribe, send an email to:Sprinklerforum-
> > [email protected]
> > > (Put the word unsubscribe in the subject field)
> >
> > --
> > Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road
> > Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> > [email protected]
> > (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to