Agree. Not required even though we usually provide valves with tamper switches.
John Sent from my BlackBerry® smartphone with Nextel Direct Connect -----Original Message----- From: Greg McGahan <[email protected]> Sender: <[email protected]> Date: Thu, 2 Dec 2010 16:39:41 To: <[email protected]> Reply-To: <[email protected]> Subject: Re: tamper switches *4.25.5.7* 2010 edition - the JP Isolation valves are NOT required to be supervised. On 12/2/2010 3:48 PM, Ed Kramer wrote: > Are suction and discharge valves of a jockey pump required to be supervised? > Section 5.16.1 (NFPA 20 2007) says 'yes', but doesn't clarify if its > intended to apply to both fire pumps and jockey pumps. Anybody want to > speculate on the intent? I've always put tamper switches on them, but now > I'm wondering if it's required or not. > > > > Ed Kramer > > Littleton, CO > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) -- Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)