*4.25.5.7* 2010 edition - the JP Isolation valves are NOT required to be supervised.

On 12/2/2010 3:48 PM, Ed Kramer wrote:
Are suction and discharge valves of a jockey pump required to be supervised?
Section 5.16.1 (NFPA 20 2007) says 'yes', but doesn't clarify if its
intended to apply to both fire pumps and jockey pumps.  Anybody want to
speculate on the intent?  I've always put tamper switches on them, but now
I'm wondering if it's required or not.



Ed Kramer

Littleton, CO