*4.25.5.7* 2010 edition - the JP Isolation valves are NOT required to
be supervised.
On 12/2/2010 3:48 PM, Ed Kramer wrote:
Are suction and discharge valves of a jockey pump required to be supervised?
Section 5.16.1 (NFPA 20 2007) says 'yes', but doesn't clarify if its
intended to apply to both fire pumps and jockey pumps. Anybody want to
speculate on the intent? I've always put tamper switches on them, but now
I'm wondering if it's required or not.
Ed Kramer
Littleton, CO
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
--
Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road
Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)