Thanks, Greg.  Looks like it's time to update my NFPA 20.

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Greg McGahan
> Sent: Thursday, December 02, 2010 3:40 PM
> To: [email protected]
> Subject: Re: tamper switches
> 
> *4.25.5.7*  2010 edition  - the JP Isolation valves are NOT required to
> be supervised.
> 
> 
> On 12/2/2010 3:48 PM, Ed Kramer wrote:
> > Are suction and discharge valves of a jockey pump required to be
> supervised?
> > Section 5.16.1 (NFPA 20 2007) says 'yes', but doesn't clarify if its
> > intended to apply to both fire pumps and jockey pumps.  Anybody want
> to
> > speculate on the intent?  I've always put tamper switches on them, but
> now
> > I'm wondering if it's required or not.
> >
> >
> >
> > Ed Kramer
> >
> > Littleton, CO
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> > (Put the word unsubscribe in the subject field)
> 
> --
> Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road
> Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to