You would also need to see how the back pressure would affect the valve's 
ability to discharge.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, December 07, 2010 10:00 AM
To: [email protected]
Subject: RE: Pumps - PRV Piped Back to Source

I've seen PRV discharge sent to storm sewer, sent to ditch and sent back to 
water storage tank. If it could be re-introduced back into the suction supply, 
can't imagine what that would do to system hydraulics.


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Tuesday, December 07, 2010 10:21 AM
To: [email protected]
Subject: Pumps - PRV Piped Back to Source

Hello,
When NFPA #20 requires a pressure relief valve in accord with 5.18.1.1 for a 
diesel pump is it an acceptable practice to pipe the PRV discharge piping back 
to the source piping? The source is a city water main. I see NFPA 20 has some 
info on this but I've never seen it done and was wondering if this would be 
designed similar to a flow meter test loop?

Thanks,
Ralph





      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to